[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] question about air-air heat recovery wit h economizer
The prior message was posted by mistake. Please disregard
-----Original Message-----
From: Dobbs, Gregory M UTRC [mailto:dobbsgm@xxxxxxxxxxxx]
Sent: Friday, November 05, 2004 10:06 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] question about air-air heat recovery wit h
economizer
My runs for New York WITHOUT ERV show heating energy with economizer higher
than without economizer. Is this true for you also? Do you agree? If so,
do you understand why this is happening?
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/