Re: [EnergyPlus_Support] swimming pool
I do not believe that you can perform a swimming pool study with Energy+
unless you become a developer and write some code of your own. There
are no provisions for integrating the variable water evaporation rates
of the pool water surface other than specifying loads in schedules. The
available mechanical equipment can not be controlled to mimic available
pool HVAC equipment. In any simulation, the ground heat losses can be
highly variable. That said, I was able to use Energy+ to calculate some
design loads for a small natatorium. Under design conditions one can
specify reasonable moisture loads and discharge conditions from the
equipment so that purchased air can be used. The task I had for my
simulation was to predict a summer cooling condition given the existing
equipment and a row of trees a few yards away from a new solarium that
formed one end of the pool space...
Ned Lyon
Senior Project Manager
Simpson Gumpertz & Heger Inc.
41 Seyon Street
Building #1, Suite 500
Waltham, MA 02453
Phone: 781-907-9000
Fax: 781-907-9009
>>> Roberto.Lollini@xxxxxxxxxx 11/10/2004 11:47:52 AM >>>
Dear all, I have to carry out an energy diagnosis of a sport building
including a swimming pool. I would like to know if is it possible to
simulate it by EnergyPlus, I mean the energy consumption of the
swimming
pool as a function of water temperature, water amount ... also
considering
the very wet indoor ambient (very high ambient RH and high ambient
temperature).
Thank you very much for your attention.
Regards,
Roberto Lollini
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
Yahoo! Groups SponsorADVERTISEMENT
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/