At 03:37 AM 12/3/2004, Ali_Ajmi wrote:
>I have run the attached file " fiveZoneDXVAVallconst (if can't be
>accesses, will be accesses in the file folder) but many sever errors
>generated which i could not understand. Pleas could any, run it using E+ v
>1.1.1 and explain to me what these errors mean.
>
These are your biggest problem:
** Severe ** Did not find matching material for construct MW PARTITION
WALL, missing material = PLASTER MWP
** Severe ** Did not find matching material for construct MW PARTITION
WALL, missing material = CONCRETE BLOCK MWP
** Severe ** Did not find matching material for construct MW PARTITION
WALL, missing material = PLASTER MWP
These cause the program to stop. You have material objects and properties
for these materials (PLASTER MWP and CONCRETE BLOCK MWP).
The others are more of an alert -- to make sure you know what you are doing
when you input something like that:
** Severe ** CAUTION -- Interzone surfaces are usually in different zones
** ~~~ ** Surface=ZONE NORTH SURFACE WEST, Zone=ZONE NORTH
** ~~~ ** Surface=ZONE NORTH SURFACE EAST, Zone=ZONE NORTH
Here, you've said that the surface (Zone North Surface West) is adjacent to
another surface in that same zone (Zone North Surface East). That may be
okay if you understand the consequences of setting up your model with that
adjacency.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/