Mike,

Thanks for looking at that.

So, this is news. A "mixture of autosized and user-specified 
values...generally does not work well". 

Is this even when the EIO file reports correct/acceptable values for 
all the autosized parameters?

Just as a comment, the I/O Reference certainly does not lead one to 
believe this is the case, the way it is written it seems to encourage 
the use of autosizing. 

Shaun


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@g...> wrote:
> It is difficult to evaluate what is happening here, because the 
file is a 
> mixture of autosized and user-specified values.  This generally 
does not work 
> well in EnergyPlus.  
> 
> The supply air temperature not meeting setpoint appears to be a 
problem with 
> the cooling coil inputs.  Within COIL:WATER:COOLING, the coil 
should be allowed 
> to completely autosize or be completely specified.  Also, there is 
more outside 
> air flow specified in the outside air controller than in the ZONE 
SIZING 
> object.  Finally, try using COIL:Water:DetailedFlatCooling to see 
if that will 
> adequately control the supply air temperature.
> 
> Mike
> 
> 
> On 8 Dec 2004, at 2:45, sm278424 wrote:
> 
> > 
> > 
> > Hi Mike,
> > 
> > I've uploaded a couple of files (an EPMIDF and an XLS with some 
of 
> > our results). Your response leaves me puzzled because the zone 
> > setpoint is not being met, yet
> >   -> unmet demand = 0
> >   -> the chilled water coil deltaT at peak is only 2.4C when 5.6C 
is 
> > design/idf input
> >   -> the SA volume is fixed at 73 L/s (more than the bare minimum)
> >   -> the SA temperature is too warm because E+ says it has to be 
> > warmer (11.67C is idf input)
> >   -> the radiant panel flow is not at capacity
> > 
> > I wonder if you could see if you see any problems with our IDF 
input.
> > 
> > About your earlier question, I'm using COIL:Water:Cooling.
> > 
> > Shaun
> > 
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> > <mjwitte@g...> wrote:
> > > If the unmet demand is zero, then the plant has enough capacity 
to 
> > meet the 
> > > request from the chilled water coil.  If the zone setpoint is 
still 
> > not met, 
> > > then the chilled water coil is not delivering enough cooling.  
> > Either the 
> > > airflow rate is too low, or the supply air temperature is too 
> > warm.  This could 
> > > be a control problem, an airflow sizing problem, or a coil 
sizing 
> > problem.
> > > 
> > > Mike
> > > 
> > > 
> > > On 4 Dec 2004, at 0:40, sm278424 wrote:
> > > 
> > > > 
> > > > 
> > > > Thanks Mike,
> > > > 
> > > > Can I ask one further question re: zone temperatures and 
unmet 
> > demand.
> > > > 
> > > > If the unmet demand is zero, then I should have enough 
capacity 
> > in 
> > > > the plant loop.  
> > > > 
> > > > I have a fixed zone cooling setpoint of 23C.  But in some of 
our 
> > > > simulations we see zone air temperatures that are several 
degrees 
> > > > above our setpoint.  If the capacity is there, why would my 
zone 
> > air 
> > > > temp be off the setpoint?
> > > > 
> > > > Thanks again,
> > > > Shaun Martin
> > > > 
> > > > 
> > > > 
> > > > 
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> > > > <mjwitte@g...> wrote:
> > > > > 1.  If the air loop outlet setpoint is not being met, then 
the 
> > coil 
> > > > capacity or 
> > > > > chilled water flow rate or chiller capacity is not 
adequate.  
> > Which 
> > > > cooling 
> > > > > coil model are you using?  Use COIL:Water:Cooling or 
> > > > > COIL:Water:DetailedFlatCooling.  COIL:Water:SimpleCooling 
does 
> > not 
> > > > always 
> > > > > deliver adequate capacity under certain conditions (this 
model 
> > will 
> > > > not be 
> > > > > available in the next release).
> > > > > 
> > > > > 2.  It is very difficult to get a hybrid forced air/radiant 
> > system 
> > > > to behave as 
> > > > > desired with current EnergyPlus control options.  In your 
case, 
> > if 
> > > > you want the 
> > > > > radiant system to modulate, then why use a VAV air system?  
> > Perhaps 
> > > > a constant 
> > > > > volume system would be better.  Also, you should set the 
air 
> > system 
> > > > to run as 
> > > > > the first cooling priority, so the radiant system can pick 
up 
> > the 
> > > > remaining 
> > > > > load.  Alternatively, perhaps the VAV system is oversized?  
If 
> > it 
> > > > is sized 
> > > > > smaller so that it cannot meet the entire cooling load, 
then it 
> > > > will open to 
> > > > > full flow, thus supplying a constant volume of air.
> > > > > 
> > > > > 3.  With cool surfaces for radiant slabs, it would be 
expected 
> > that 
> > > > comfort is 
> > > > > maintained at higher dry bulb temperatures.  Check all of 
the 
> > > > comfort inputs to 
> > > > > make sure thay are appropriate (clothing, activity level, 
air 
> > > > velocity).
> > > > > 
> > > > > 4.  These unmet demands are why #1 is happening.  The 
chiller 
> > plant 
> > > > is not able 
> > > > > to meet the load, so the chilled water supply temperature 
> > rises, 
> > > > and then the 
> > > > > coil cannot meet the supply air setpoint.  Everything is 
> > > > simultaneous in 
> > > > > EnergyPlus, so unmet demands result in unmet setpoints.
> > > > > 
> > > > > 5.  Zone/Sys Sensible Heating (and Cooling) do not include 
> > radiant 
> > > > slab system 
> > > > > loads.  (I see we need to clarify the definition of this, 
or 
> > change 
> > > > the way it 
> > > > > is reported.)  Also, if there is outside air, that will 
place a 
> > > > load on the 
> > > > > cooling coil which is not included in the load delivered to 
the 
> > > > zone.
> > > > > 
> > > > > Mike
> > > > > 
> > > > > 
> > > > > On 1 Dec 2004, at 20:48, sm278424 wrote:
> > > > > 
> > > > > > 
> > > > > > 
> > > > > > Hi, again,
> > > > > > 
> > > > > > I'm modeling a single zone with a VAV system and a 
radiant 
> > panel. 
> > > > I 
> > > > > > control the mixed air temp, HC water inlet and CC water 
inlet 
> > > > with 
> > > > > > the AIR LOOP OUTLET node, which is controlled by a 
SETPOINT 
> > > > MANAGER 
> > > > > > to a setpoint of 12.2C.
> > > > > > 
> > > > > > What happens at peak cooling load is both the radiant 
panel 
> > and 
> > > > the 
> > > > > > VAV box go to full flow, and E+ allows the AIR LOOP 
OUTLET 
> > > > > > temperature to modulate.
> > > > > > 
> > > > > > 
> > > > > > My questions:
> > > > > > 
> > > > > > 1. Is there any way to lock in the AIR LOOP OUTLET temp 
in 
> > order 
> > > > to 
> > > > > > allow the supply volume to vary? 
> > > > > > 
> > > > > > 2. Can the supply temp and volume both be locked at 
specific 
> > > > values, 
> > > > > > so that the radiant panel modulates more fully?  Can you 
> > suggest 
> > > > > > appropriate radiant panel schedules for this? 
> > > > > > 
> > > > > > 3. In our models we've seen the FANGER PMV produce PPD 
values 
> > of 
> > > > > > between 6-10% when zone mean air temperatures are 
relatively 
> > high 
> > > > eg 
> > > > > > 77-79F (the PPD formula is from the Engineering doc).  
Does 
> > this 
> > > > make 
> > > > > > sense to you?  The comfort band seems too wide, in most 
> > buildings 
> > > > > > complaints start flowing whenever zone DB temperatures 
exceed 
> > 75F.
> > > > > > 
> > > > > > 4. When we get UNMET DEMAND on our plant loops in these 
> > > > simulations, 
> > > > > > the values are very high, much more than the total zone 
loads 
> > > > would 
> > > > > > ever be. We can't explain the values.
> > > > > > 
> > > > > > 5. With this model the total zone load is the rad panel 
> > cooling 
> > > > rate 
> > > > > > + the CC rate, but the Zone/Sys Cooling Rate values are 
all 
> > over 
> > > > the 
> > > > > > place (but usually quite low). Why should this be?  
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > Thanks
> > > > > > Shaun Martin
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > The primary EnergyPlus web site is found at:
> > > > > > http://www.energyplus.gov
> > > > > > 
> > > > > > The group web site is:
> > > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > > > 
> > > > > > Attachments are not allowed -- please post any files to 
the 
> > > > appropriate folder
> > > > > > in the Files area of the Support Web Site.
> > > > > > 
> > > > > > Yahoo! Groups Links
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > 
> > > > > 
> > > > > 
> > > > > ========================================================
> > > > > Michael J. Witte, GARD Analytics, Inc.
> > > > > EnergyPlus Testing and Support      
> > > > > EnergyPlus-Support@g...
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > > 
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > 
> > > > Attachments are not allowed -- please post any files to the 
> > appropriate folder
> > > > in the Files area of the Support Web Site.
> > > > 
> > > > Yahoo! Groups Links
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > >
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/