RE: [EnergyPlus_Support] Internal Loads
Your difference is probably caused by using a radiant load for internal
gain. Purchased air is only going to balance convective loss. My guess
is that you may see some slightly different surface temperatures in your
model and if you change the load to 0% radiant, the energy will balance.
________________________________
From: Wilde, Pieter de [mailto:P.deWilde@xxxxxxxxxxx]
Sent: Sunday, December 12, 2004 9:37 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Internal Loads
Dear list-members,
I have a question about internal gains. I am currently running a simple
building (1 zone) under the climate of Stockholm. Internal gains are
modeled as "other equipment", 300 Watt, 100% radiant. The schedule for
this equipment is "on" all the time. I want to calculate heating loads,
using the Purchased Air System. What is puzzling me is the following:
If I run the file I can see the heating is working all the time in
January, February etc as the indoor temperature is constantly my
setpoint value of 20 degrees Celcius, and the heating energy is pretty
constant. Now if I turn OFF my internal loads by reducing the 300 Watt
to 0 Watt, I would expect the heating energy per timestep to increase
with 300 W x 3600 = 1080.000 J. However, the difference between heating
energy with and without internal load is only about 930.000 J. No other
mods were made between these two runs. In the file without internal
loads the temperature is 20 degrees as well, so all internal gains
should contribute to the heating.
Does anybody have a pointer to what might be causing this? May-be
something in the Purchased Air approach, or???
Thanks for any advice!
Best regards,
Pieter de Wilde
P.J.C.J. (Pieter) de Wilde
TNO Building and Construction Research
Email: P.deWilde@xxxxxxxxxxx
Phone: +31 15 276 3520
Fax: +31 15 276 3023
Visiting Address:
Van Mourik Broekmanweg 6
2628 XE Delft
The Netherlands
Postal Address:
P.O. Box 49
2600 AA Delft
The Netherlands
http://www.bouw.tno.nl
The disclaimer that applies to e-mail from TNO Building and Construction
Research can be found on http://www.tno.nl/disclaimer/email.html
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
Yahoo! Groups Sponsor
ADVERTISEMENT
click here
<http://us.ard.yahoo.com/SIG=129hnfck2/M=298184.5639630.6699735.3001176/
D=groups/S=1705007389:HM/EXP=1102948657/A=2434971/R=0/SIG=11eeoolb0/*htt
p://www.netflix.com/Default?mqso=60185400>
<http://us.adserver.yahoo.com/l?M=298184.5639630.6699735.3001176/D=group
s/S=:HM/A=2434971/rand=446308277>
________________________________
Yahoo! Groups Links
* To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
* To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
be>
* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service <http://docs.yahoo.com/info/terms/> .
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
$4.98 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/Q7_YsB/neXJAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/