What kind of system is serving the direct air terminal unit?  Is it a fixed 
supply air temperature?  The only way to control the amount of heating and 
cooling provided by direct air is to use a set point manager such as SET POINT 
MANAGER:COLDEST.  If I understand your intent correctly, the direct air unit 
should be priority 1 so it will run first, then the fan coil should be priority 
2 so it will pick up any remaning load.  Perhaps the direct air flow was 
meeting the entire load (or more) and that is why the fan coil would not 
operate?

Mike

On 24 Dec 2004, at 2:55, zyyh9819 wrote:

> 
> 
>   Thank you very much for your reply for my question about
> sunflower2.idf! I have another question. 
>   I would like to simulate a building with Fan coil and direct air. 
> In Zone Equipment List of my idf file, I define the direct air with 
> the highest cooling and heating priority and the fan coil with the 
> next highest priority.
>   But in the result, I find the direct air can not work. Then I 
> define the fan coil with the highest cooling and heating priority 
> and the direct air with the next highest priority. At this time, I 
> find the fan coil can not work. I can not explain it. me! please 
> help me. I will very appreciate it!
> 
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$4.98 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/Q7_YsB/neXJAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/