Surfaces should face out from a zone and the vertices are entered when looking 
at the surface from the outside.  The error message indicates that both of 
these surfaces are facing 270.  One of them should be facing 90.  "report, 
surfaces, details;" produces a listing of all surfaces with azimuth, tilt, 
area, etc., in the eio output file.  This can be helpful in checking geometry 
inputs.  

Mike  

On 4 Jan 2005, at 22:41, mshirong wrote:

> 
> 
> I find the following warning in err file. I check out it again, But find the
> order of vertexentry is right as others. Could you tell me what is wrong?
> Thanks!
> 
> Program Version,EnergyPlus 1.2.1.022, 2005-1-4 22:20,IDD_Version 1.2.1.022
>    ** Warning ** InterZone Surface Azimuths do not match as expected.
>    **   ~~~   **   Azimuth=270.0 in Surface=ZN003:WALL003, Zone=EPZONE
>    **   ~~~   **   Azimuth=270.0 in Surface=ZN002:WALL003, Zone=WPZONE
>    ************* Testing Individual Branch Integrity
>    ************* All Branches passed integrity testing
>    ************* Testing Individual Supply Air Path Integrity
>    ************* All Supply Air Paths passed integrity testing
>    ************* Testing Individual Return Air Path Integrity
>    ************* All Return Air Paths passed integrity testing
>    ************* No node connection errors were found.
> 
> 
> Meng
> 
> 
> 
> 
> ---------------------------------
> Do You Yahoo!?
> 150ÍòÇúMP3·è¿ñËÑ£¬´øÄú´³ÈëÒôÀÖµîÌÃ
> ÃÀÅ®Ã÷ÐÇÓ¦Óо¡ÓУ¬ËѱéÃÀͼ¡¢ÑÞͼºÍ¿áͼ
> 1G¾ÍÊÇ1000Õ×£¬ÑÅ»¢µçÓÊ×ÔÖúÀ©ÈÝ£¡
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/