Re: [EnergyPlus_Support] thermal comfort
1. See Engineering Reference section on Thermal Comfort, beginning on p. 447
(pdf p. 485).
2. In order to determine heating and cooling loads in EnergyPlus, you need to
specify temperature controls and some type of HVAC system. The simplest system
is "purchased air" which is an infinite supply of hot and cold air. This can
be used to calculate loads without specifying a full HVAC system. There is a
sample file called "PurchAir.idf" in the EnergyPlus\ExampleFiles folder which
will show you the objects required. To determine approximate envelope loads,
run a simulation with no internal gains.
Mike
On 10 Feb 2005, at 2:59, mohammed khaylani wrote:
>
> hi
> i am fine with E+ but i need to now 2 things:
> 1) which variables are usually used to measure thermal comfort for the building
> occupants 2) if i want to know the total energy which will be recieved by the
> zone from the natural environment(sun wind....etc) ignoring occupants,lights
> and electric equipments WHAT shall i do? what can i use to measure it? thanks
> mohammed s. khaylani
>
>
>
> ---------------------------------
> Do you Yahoo!?
> Yahoo! Search presents - Jib Jab's 'Second Term'
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/