in my mail I wanted to know what are the conventions for internal
surfaces.
These surfaces are located in the room. For e.g. a kind of balcony or
gallery .
One room with two levels.
 
Thanks.
Arno
 
 
 
 
-----Ursprüngliche Nachricht-----
Von: Michael J. Witte [mailto:mjwitte@xxxxxxxx] 
Gesendet: Freitag, 4. Februar 2005 00:28
An: EnergyPlus_Support@xxxxxxxxxxxxxxx
Betreff: Re: [EnergyPlus_Support] Internal surface
 
Each internal surface is described twice - once in each of the zones it 
separates.  The first layer in a construction is always the outside
layer 
relative to the zone it is attached to.  Within a zone, the inside layer

absorbs solar radiation which has entered the zone through windows.  See

example file 5ZoneAuto.idf  It has five zones plus a plenum zone with
interzone 
surfaces between all zones

Mike


On 1 Feb 2005, at 16:51, Arno Dentel wrote:

> 
> Hello.
> What are the conventions to model an internal surface:
> What is the inside or outside layer of the construction?
> Especially you have a horizontal surface. 
> Which side of the surface absorbs the beam radiation?
> And what kind of surface type is it: a ceiling or a floor?
> Thanks - Arno.
> 
> 
> 
> 
> 
> ______________________________________________________
> Arno Dentel
> Georg-Simon-Ohm Fachhochschule Nürnberg
> Institut für Energie und Gebäude - ieg
> Keßlerplatz 12
> 90489 Nürnberg
> Tel:  +49 - 911 - 5880 -1846
> Fax: +49 - 911 - 5880 -5846
> 
> E-Mail: arno.dentel@xxxxxxxxxxxxxxx
> web: www.ieg.fh-nuernberg.de
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.




  _____  

Yahoo! Groups Links
*         To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
  
*         To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
be> 
  
*         Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service <http://docs.yahoo.com/info/terms/> . 


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/