[EnergyPlus_Support] Re: CO2 buildup control





Hi,

Yeah, I have everything laid out as you have specified below. The 
file itself is uploaded in the Files section of the website named 
AHU3_BenchmarkMetricMV.idf. The additions I made when trying to add 
this object is:

* Mechanical:Ventilation object 
* Reference to the Mechanical:Ventilation object in the Outside Air 
Controller
* A list of two zones: "zFlr3MediaRoom & zFlr3CloseControl" 
referenced by the Mechanical:Ventilation object

Have I missed anything, I have looked through the 
HeatPumpSimpleDCV.idf example, but I cannot spot how my file 
differs. 

Kind regards

-Elmer



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "donbshireyiii" 
<shirey@f...> wrote:
> 
> Is Controller:Outside air = AHU3 OA CONTROLLER in a CONTROLLER 
LIST,
> and is the CONTROLLER LIST name specified in the OUTSIDE AIR SYSTEM
> (Name:Controller list) used by the air loop serving Zone name =
> ZFLR3CLOSECONTROL?
> 
> Look carefully at the example file HeatPumpSimpleDCV.idf to see the
> required relationships among these objects.
> 
> If this fails to fix your problem, upload your idf file to Files 
area
> of EnergyPlus_Support@xxxxxxxxxxxxxxx, or send the file as an e-
mail
> attachment to EnergyPlus-Support@g...
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Elmer Morrissey"
> <elmofuddly@y...> wrote:
> > 
> > Thank you for your help,
> > 
> > I instantiated a ventilation:mechanical into my idf file?
> > 
> > 
> > VENTILATION:MECHANICAL,
> >     MechVentController,      !- Mechanical ventilation object 
name
> >     Plant Workhours Sched,   !- Availability schedule name
> >     AHU3 Serviced Zones,     !- Zone name 1
> >      .001,                   !- Ventilation rate per unit floor
> area 
> > 1 {m3/s-m2}
> >      .012;                   !- Ventilation rate per occupant 1 
> > {m3/s-person}
> > 
> > However, I retrieved the following warning?
> > 
> >    ** Warning ** Zone name = ZFLR3CLOSECONTROL in 
> > VENTILATION:MECHANICAL object name = MECHVENTCONTROLLER is not 
on 
> > the same air loop as Controller:Outside air = AHU3 OA CONTROLLER
> >    **   ~~~   ** This zone will not be used and the simulaiton 
will 
> > continue...
> > 
> > Thus, my mechanical controller is no longer working. The zone 
> > highlighted in the warning IS serviced by that AHU so can anyone 
> > recognise an area of focus to fix this problem?
> > 
> > Kind regards
> > 
> > -Elmer Morrissey
> > 
> > 
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "donbshireyiii" 
> > <shirey@f...> wrote:
> > > 
> > > In addition, see the example file HeatPumpSimpleDCV.idf
> > > 
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
> > > <RRaustad@F...> wrote:
> > > > Use the Ventilation:Mechanical object. It determines outdoor
> air 
> > > > requirements based on floor area or number of occupants 
served 
> > by an
> > > air 
> > > > loop. See IO Ref and Eng Doc for further details.
> > > > 
> > > > Elmer Morrissey wrote:
> > > > 
> > > > >
> > > > > Hello,
> > > > >
> > > > > Is there any means of controlling CO2 buildup in a space 
and
> > > thereby
> > > > > controlling recirculated air in the zone?
> > > > >
> > > > > Kind regards
> > > > >
> > > > > Elmer D. Morrissey,
> > > > > Informatics Researach Unit for Sustainable Engineering
> (IRUSE),
> > > > > Department of Civil & Environmental 
Engineering/Environmental
> > > Research
> > > > > Institute (ERI),
> > > > > National University of Ireland, Cork (UCC),
> > > > > Ireland.
> > > > >
> > > > > ph:    00-353-21-490-2913
> > > > > mob: 00-353-87-231-5382
> > > > > fax:  00-353-21-427-7648





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/