[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Downloading Version 1.2.1
Does anyonoe know if there's a way to reinstall Version 1.2.1 after
installing V1.2.2?
None of my files work with the new version, and I need to run them to
produce a report that's due at the end of next week.
I ran the transition program and manually fixed many errors, but any
files with Hot Water Loops generate the following error.
** Severe ** Inlet parameters for plant demand side splitter are not
physically possible **
** Problem in input for plant demand side HOT WATER LOOP **
** The maximum flow out of the splitter is less than the minimum inlet
flow **
** Flow rate inputs for the loop do not match flow requirements of the
various branches/components **
** Check your flow rates and make sure that flow balances between the
splitter inlet and outlets
None of my flow rates are being autosize, and I have made sure all the
inlet flows equal the outlet flows. Has anyone else had this problem
with the new version? I read some other messages about this same
error, but the folks were able to fix it using V1.2.1 - my files all
ran fine with the older version, so if anyone knows where to get the
old version, I would appreciate it!
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/