[EnergyPlus_Support] Re: EIR Chiller Performance Curve Fitting
Dear Sam
I am studying in developing an absorption chiller which can use the recovery heat from
chillers and engines. I reseach the chiller modules for the purpose. What will you do in
shanghai? And who will you work for?
charlie
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee <samwslee@y...> wrote:
> Hi,
>
> Which course or module that you are studying? May be I have a chance to work at
Shanghai at the end of this year.
>
> SAM
>
> applezealot <applezealot@y...> »¡?G
> Dear Sam
>
> I am a gradute student in Shanghai Jiaotong University. If you
> have the problem of reading Chinese,it will be alright that we could
> still discuss in English. Thank you very much for your patient and
> help. We start using the software about half a year. And I need to
> use E+ to complete my thesis. So I won't hesitate to ask you for your
> help if I get into trouble with E+
> Best wishes
> See you
> charlie
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee
> <samwslee@y...> wrote:
> > Hi,
> >
> > Ok, but I type Chinese Word very slowly and I worry about that I
> can see the simplified words in my computer. May be you can try it!
> >
> > I live in Hong Kong and work at Government Department, so I have
> chance to use EnergyPlus to simulate various Government property in
> Hong Kong. Since I have successfully simulate two nos of the
> Government Buildings, those simulation results can reflect the actual
> energy use.
> >
> > If you have any problem, please don't hesitate to discuss with me.
> >
> > **Which university you study?
> >
> > SAMLEE
> >
> > applezealot <applezealot@y...> »¡?G
> > Dear Sam
> > Thank you very much for your help. And nice meeting you
> through
> > the internet. I am a graduate student in shanghai studying E+ for
> > about 4 months. Are you a chinese too? Maybe we speak our lanaguage
> > to discuss the issues about the software.
> > Is that OK for you?
> >
> > charlie
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee
> > <samwslee@y...> wrote:
> > > Hi Charlie,
> > >
> > > As compare between predicted simulation result and the actual
> > energy use, the error is within 5%. So it is realistic.
> > >
> > > SAMLEE
> > >
> > > applezealot <applezealot@y...> »¡?G
> > > Hi Sam
> > > I gott you. But I am not sure that the third curve you defined
> > is
> > > able to simulate the chiller performance. Since you have done
> some
> > > work on the chiller module, does the results show the correctness?
> > > Thank you very much for your help
> > >
> > > charlie
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee
> > > <samwslee@y...> wrote:
> > > > Hi Charlie,
> > > >
> > > > As you know 1) the PRL is equal to the rated cooling load
> divided
> > > by the available cooling load. e.g. from the manufacture, tha
> > > standard rating for the specific leaving chilled water
> temperature
> > > (6.7oC) and the entering air temperature (35oC).
> > > > 2) the value ChillerEIRFPLR (Y) is EIRavailable / (EIRdesign x
> > > PRL). You can refer to the EngineeringDoc P.338.
> > > >
> > > > SAMLEE
> > > >
> > > > applezealot <applezealot@y...> »¡?G
> > > > Dear sam
> > > >
> > > > I check your excel file. I have some question about your
> > > > calculation:
> > > > 1. You used (Qr/Qa) as PLR and (Pa/Pr) as EIR output ratio
> for
> > > the
> > > > third.I get confused about these settings. Could you please
> tell
> > > me
> > > > why you choose these parameters? P.S. Pa,Pr,Qa,Qr are power
> > > > available, power rated, capacity available and capacity rated.
> > > > 2. And I look into the curve fitting results in sheet1 of
> your
> > > > file. Is it related to our discussion? I can not understand
> the
> > > > purpose of this sheet. Please explain it for me.
> > > >
> > > > Thank you in advance
> > > > charlie
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee
> > > > <samwslee@y...> wrote:
> > > > > Hi,
> > > > >
> > > > > Please go here
> > > >
> > >
> >
> http://groups.yahoo.com/group/EnergyPlus_Support/Files/Problem_Submit
> > > > tals/Input Problem/Fit curve biquadratic d.xls
> > > > >
> > > > > It seems to be corrected and solved
> > > > >
> > > > > SAMLEE
> > > > >
> > > > >
> > > > > donbshireyiii <shirey@f...> ¼¶?g:
> > > > > Charlie and SAMLEE,
> > > > >
> > > > > In the spreadsheet you are using, it looks like EIR as a
> > function
> > > > > of PLR is not being properly calculated.
> > > > >
> > > > > The spreadsheet seems to be using available capacity at the
> > > current
> > > > > operating conditions divided by the design (rated) capacity
> of
> > > the
> > > > > chiller. This is not correct.... is should be just as the
> > > > > input/output reference says... PLR = (cooling load) divided by
> > > > > (available capacity at the current operating conditions).
> > > > >
> > > > > Don
> > > > >
> > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee
> > > > > <samwslee@y...> wrote:
> > > > > > Hi Charlie,
> > > > > >
> > > > > > I just use your advice that the PRL shoudl equal to the
> ratio
> > > of
> > > > > cooling load to the available capacity.
> > > > > > Please see my attached file at
> > > > > http://groups.yahoo.com/group/EnergyPlus_Support/F
> > > > > iles/Problem_Submittals/Input
> > > > > Problem/Fit curve biquadratic b.xls
> > > > > >
> > > > > > SAMLEE
> > > > > >
> > > > > > energypluser <energypluser@y...> ¼¶?g:
> > > > > > Dear Mike,
> > > > > >
> > > > > > I wanna simulate a electric chiller with the EIR
> module.
> > > > And I
> > > > > > found that you give a EXCEL example for the curve fitting.
> > But
> > > I
> > > > > think
> > > > > > the third curve in your example file may not be correct.
> > > > > > According to the input/output reference, the third
> curve
> > > is
> > > > > the
> > > > > > EIR output ratio in function of Part Load Ratio. The PLR
> > > > > calculation in
> > > > > > your file is the ratio of the available capacity to the
> > > nominal
> > > > > > capacity. In my opinion, PLR should equal to the ratio of
> the
> > > > > cooling
> > > > > > load to the available capacity. Am I right?
> > > > > > If I am right, could you please tell me how to obtain
> > the
> > > > > third
> > > > > > curve for my simulation based on the manufacturer catalog.
> > > > > > Thank you in adavance
> > > > > >
> > > > > >
> > > > charlie
> > > > >
> > > > >
> > > > >
> > > > >
> > > > > The primary EnergyPlus web site is found at:
> > > > > http://www.energyplus.gov
> > > > >
> > > > > The group web site is:
> > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > >
> > > > > Attachments are not allowed -- please post any files to the
> > > > appropriate folder in the Files area of the Support Web Site.
> > > > >
> > > > >
> > > > >
> > > > >
> > > > > ---------------------------------
> > > > > Yahoo! Groups Links
> > > > >
> > > > > To visit your group on the web, go to:
> > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > >
> > > > > To unsubscribe from this group, send an email to:
> > > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > > >
> > > > > Your use of Yahoo! Groups is subject to the Yahoo! Terms
> of
> > > > Service.
> > > > >
> > > > >
> > > > >
> > > > > ---------------------------------
> > > > > ?Q?Y?¦¬??s email ?q??H
> > > > > ?U¸ü Yahoo! Messenger
> > > > > http://messenger.yahoo.com.hk
> > > > >
> > > > > [Non-text portions of this message have been removed]
> > > >
> > > >
> > > >
> > > >
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > >
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > >
> > > > Attachments are not allowed -- please post any files to the
> > > appropriate folder in the Files area of the Support Web Site.
> > > >
> > > >
> > > >
> > > >
> > > > ---------------------------------
> > > > Yahoo! Groups Links
> > > >
> > > > To visit your group on the web, go to:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > >
> > > > To unsubscribe from this group, send an email to:
> > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > >
> > > > Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > > Service.
> > > >
> > > >
> > > >
> > > >
> > > > ---------------------------------
> > > > ?Q?Y?¦¬??s email ?q??H
> > > > ?U¸ü Yahoo! Messenger
> > > > http://messenger.yahoo.com.hk
> > > >
> > > > [Non-text portions of this message have been removed]
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files area of the Support Web Site.
> > >
> > >
> > >
> > >
> > > ---------------------------------
> > > Yahoo! Groups Links
> > >
> > > To visit your group on the web, go to:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > > Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > Service.
> > >
> > >
> > >
> > > ---------------------------------
> > > ?Q?Y?¦¬??s email ?q??H
> > > ?U¸ü Yahoo! Messenger
> > > http://messenger.yahoo.com.hk
> > >
> > > [Non-text portions of this message have been removed]
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
> >
> >
> >
> >
> > ---------------------------------
> > Yahoo! Groups Links
> >
> > To visit your group on the web, go to:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> Service.
> >
> >
> >
> > ---------------------------------
> > ?Q?Y?¦¬??s email ?q??H
> > ?U¸ü Yahoo! Messenger
> > http://messenger.yahoo.com.hk
> >
> > [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the
Files area of the Support Web Site.
>
>
>
>
> ---------------------------------
> Yahoo! Groups Links
>
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
>
> ---------------------------------
> ?Q?Y?¦¬??s email ?q??H
> ?U¸ü Yahoo! Messenger
> http://messenger.yahoo.com.hk
>
> [Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/