Re: [EnergyPlus_Support] No Temperature Control



1.  SET POINT MANAGER:SINGLE ZONE MAX HUM is placing a set point on node "AHU1 
Humidifier Outlet Node", but the cooling coil contoller's control node is "AHU1 
Fan Outlet Node".  The max hum set point must be place on the same node "AHU1 
Fan Outlet Node".

2.  SINGLE DUCT:VAV:NOREHEAT will not modulate the air volume flow rate to the 
zone for heating control.  It only controls for cooling.  If you want variable 
volume heating, then use SINGLE DUCT:VAV:REHEAT with Damper Heating Action set 
to Reverse Action.

I would suggest turning on report variables for "System Node Temp", "System 
Node Humidity Ratio", "System Node Setpoint Temp", "System Node Humidity Ratio 
Min", "System Node Humidity Ratio Max", and "System Node VolFlowRate" for key 
nodes in the system to observe how the system is responding to the controls.

Mike


On 8 Jun 2005, at 10:52, civilnug wrote:

> Hi Mike,
> 
> This is my first attempt at an idf and its not working out for me. I 
> can't seem to get control of the heating and cooling coil. Its for a 
> very tightly controlled gallery storage area, which is supposed to 
> have an RH of 50% +/- 5%. I have put the idf into the problems folder, 
> it's called, AHU1_AirLoop_PurchasedPlant_V1.idf, any help would be 
> greatly appreciated.
> 
> Thanks,
> John McCarthy.
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/