Re: [EnergyPlus_Support] Re: Report of the zone load
EnergyPlus does not report a zone latent load. The latent loads from internal
gains (people and equipment) can be reported seperately, if desired. The total
latent load including infiltration and ventilation is reported as the latent
coil load on the cooling equipment. A true latent "load" calculation requires
that the zone humidity level be controlled to a specific setpoint using a
humidistat and equipment capable of such control.
Mike
On 25 Jun 2005, at 10:06, energypluser wrote:
> Dear Mike
> I have read the ref.Do you mean that the cooling load equals to the
> zone/sys sensible cooling energy? And I have another question:
> How about the latent load in the zone?
> Is it neglected by E+ when we just controll the zone temeperature?
> Thank you in advance.
>
> charles
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@g...> wrote:
> > See the descriptions for "Zone/Sys Sensible Heating Energy"
> and "Zone/Sys
> > Sensible Cooling Energy" on pp. 181-182 (pdf pp. 214-215) in the
> Input Output
> > Reference.
> >
> > Mike
> >
> >
> >
> > On 24 Jun 2005, at 0:07, energypluser wrote:
> >
> > > Dear all
> > >
> > > How can I get the cooling & heating load output of each zone
> hourly
> > > through the report variable in E+?
> > > I have studied the rdd.file, and I can not find such vairables.
> > > Is it feasible for me to sum up some report variables for the
> > > purpose?
> > > Thank you in advance
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate folder
> > > in the Files area of the Support Web Site.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@g...
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/