Ali:
The DXSystem:AirLoop object has an input for cooling coil type and name:
DXSystem:AirLoop
A6, \field Cooling coil type
\type choice
\required-field
\key COIL:DX:CoolingBypassFactorEmpirical
\key COIL:DX:CoolingHeatExchangerAssisted
\key COIL:DX:MultiSpeed:CoolingEmpirical
\key COIL:DX:MultiMode:CoolingEmpirical
A7, \field Cooling coil name
\required-field
\type object-list
\object-list CoolingCoilsDX
Each of these coil types requests performance curves for that DX Coil.
For example, COIL:DX:CoolingBypassFactorEmpirical has the following inputs:
COIL:DX:CoolingBypassFactorEmpirical,
A5 , \field Total Cooling Capacity Modifier Curve (function of
temperature)
\required-field
\type object-list
\object-list BiquadraticCurves
\note curve = a + b*wb + c*wb**2 + d*edb + e*edb**2 + f*wb*edb
\note wb = entering wetbulb temperature (C)
\note edb = drybulb temperature seen by the condenser (C)
.....
A7 , \field Energy Input Ratio Modifier Curve (function of temperature)
\required-field
\type object-list
\object-list BiquadraticCurves
\note curve = a + b*wb + c*wb**2 + d*edb + e*edb**2 + f*wb*edb
\note wb = entering wetbulb temperature (C)
\note edb = drybulb temperature seen by the condenser (C)
This DX cooling coil object requires the names of curve objects that
specify total capacity and energy input ratio (1/COP) as a function of
the air temperature entering the condenser and the wetbulb temperature
of the air entering the cooling coil. An example curve object for the
EIR modifier curve might be:
CURVE:BIQUADRATIC,
WindACEIRFT, !- Name
0.342414409, !- Coeff1 Constant
0.034885008, !- Coeff2 x
-0.000623700, !- Coeff3 x**2
0.004977216, !- Coeff4 y
0.000437951, !- Coeff5 y**2
-0.000728028, !- Coeff6 x*y
12.77778, !- minimum value of x
23.88889, !- maximum value of x
23.88889, !- minimum value of y
46.11111; !- maximum value of y
So the Curve:Biquadratic object above is evaluated every simulation time
step that the DX coil is requested to operate to determine the energy
input ratio (1/COP) of the DX cooling coil at the entering air
temperatures during that simulation time step (i.e., based on the
weather conditions specified for the simulation for the condenser
entering air temperature and the calculated cooling coil entering air
temperature).
See the IO Reference for DXSystem for more details. Also, the example
input file TermRHDXSystem.idf should be reviewed.
Don
Ali_Ajmi wrote:
> Hi Linda,
> Do you mean that the COP of the DX system will be calculated based on
> the weather condition associated with IDF file. For example if my
> weather file is representing a very hot climate where temperature may
> reach 50 C, will the performance of the cooling coil adopted to match
> that outdoor condition? Because as far as I know the COP curve
> coefficients of the DX system are generated at New York, Syracuse
> climate condition. Consequently, the energy consumption of the DX will
> be performed on that climate condition.
>
> Ali
>
> Linda Lawrie <linda@xxxxxxxxxx> wrote:
> At 08:53 AM 7/17/2005, Ali_Ajmi wrote:
> >Could any one advice of which objects in E+ need to be change if I
> >use a different than USA weather file. For instance I am using DX
> >cooling coil so I think the COP rated for the DX system need to be
> >change, but how? and what else require changing?
> >
>
> It wouldn't be due to the non-USA weather file location -- it would
> be a change needed due to climate. At least I think that's what
> you're reasoning for changing the DX cooling coil parameters
> are? You could, perhaps, autosize your system so that the objects
> are more in line with your design climatic conditions.
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/