Hi Mike
My setpoint schedule for each zone is the same. And I compared the
heating load and cooling load for a heating month and a cooling
month. For the heating month, there is no cooling load at all. So I
am confused about the net load comparasion. The most weird thing is
that the cooling loads of two cases are similiar, but the heating
load of 9 zone with no wall is 80% more than that of 3 zone.
The heating load is the total load of the building.
Can you explain it to me ?
Thank you in advance.
charlie
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> (Responding to this post rather than yesterday's posts.)
>
> There are many reasons this could happen - differences in radiant
exchange,
> differences in thermal mass effects, differences in distribution
of solar
> gains, excess heat from the interior zone heating the perimeter
zones.
> Remember, if the simulation model describes no surfaces or mixing
between the
> interior and perimeter zones (in the 9-zone case) then there is no
heat
> transfer between them. In the 3-zone case, there is convective
and radiative
> exchange between the perimeter walls and the interior surfaces and
internal
> loads. A more valid comparison is the "net load" of the two cases
over an
> entire day or year (assuming the spaces are heated and cooled to
the same
> temperature at all times), where "net load" = Heating load minus
Cooling Load.
> This should account for offsetting loads in the interior and
perimeter spaces.
>
> Mike
>
>
> On 9 Aug 2005, at 14:30, energypluser wrote:
>
> > I have divided my building into 9 zones without using interior
walls
> > as you sugguested. For the real building, there are only 3
zones.The
> > following figure shows the plan view of the floor.The center
zone is
> > uncontrolled.The north and south zone are served by purchased
air.
> > -------------------
> > | |
> > | |
> > | |
> > |-----------------|
> > | |
> > |-----------------|
> > | |
> > | |
> > | |
> > -------------------
> > For the specificaiton of perimeter zone and interior zone, the
> > following picture shows the zoning.
> >
> > -------------------
> > | perimeter |
> > |-----------------|
> > | | interior | |
> > | | | |
> > |-----------------|
> > | |
> > |-----------------|
> > | | | |
> > | | interior | |
> > |-----------------|
> > | perimeter |
> > -------------------
> >
> > The perimeter and interior zone have the same schedule and same
> > internal gains. Since there are no wall among these zones. I
suppose
> > that the load results should be close for the two situations. But
> > the heating load of the second case is larger than that of the
first
> > case. The max differenc is up to 120%.
> > Could you please tell me the reason for the difference?
> > Thank you in advance
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
------------------------ Yahoo! Groups Sponsor --------------------~-->
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12hskcjad/M=362335.6886445.7839731.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1123742070/A=2894361/R=0/SIG=13jmebhbo/*http://www.networkforgood.org/topics/education/digitaldivide/?source=YAHOO&cmpgn=GRP&RTP=http://groups.yahoo.com/">In low income neighborhoods, 84% do not own computers. At Network for Good, help bridge the Digital Divide!</a>.</font>
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/