John,
You want to use ZONE EXHAUST FAN objects. You can have more than one exhaust per zone, but not a single one that serves multiple zones.
There will also be changes in CONTROLLED ZONE EQUIP CONFIGURATION and ZONE EQUIPMENT LIST objects for the zone.
check out the example file "TermReheatZoneExh.idf"
It sounds like you have no air system conditiong the space so you may want to add MIXING objects to declare exactly where the makeup air is coming from.
Brent
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of civilnug
Sent: Tuesday, October 04, 2005 5:28 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Extraction
Hi All,
I'm trying to go about modelling various extraction fans with a
building, these are mostly in bathroom areas with flow rates of around
0.03m3/s. These area's just have extraction fans with no supply air at
all. What I want is purely an extraction fan serving a few zones, but
only an extraction fan. Any information on whether this is possible
with E+ and any help on how to get it started would be greatly
appreciated.
Many thanks,
John.
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
SPONSORED LINKS
Audit <http://groups.yahoo.com/gads?t=ms&k=Audit+program+software&w1=Audit+program+software&w2=Email+software+program&w3=Backup+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=171&.sig=60x7-DXwclLW5oH5c2SXZw> program software Email <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Audit+program+software&w2=Email+software+program&w3=Backup+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=171&.sig=JYybHjlM1oKFWuqBjPjuNQ> software program Backup <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Audit+program+software&w2=Email+software+program&w3=Backup+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=171&.sig=aBwLNzuu1o8e8EbijRBUbQ> software program
Wedding <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Audit+program+software&w2=Email+software+program&w3=Backup+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=171&.sig=OCK-p5kfZBhuoNJCBTYWAg> program software Cad <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Audit+program+software&w2=Email+software+program&w3=Backup+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=171&.sig=y0uCM50fF1o4Nn5ZdnzwQA> software program Medical <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Audit+program+software&w2=Email+software+program&w3=Backup+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=171&.sig=t-jbbrya-X3li-mccSzEhQ> software program
_____
YAHOO! GROUPS LINKS
* Visit your group " EnergyPlus_Support <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
* To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
* Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> .
_____
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/