Re: [EnergyPlus_Support] air flow limit
This is a Close control equipment that provides a unferfloor flow. the
catalog says that for standard conditions (24ºC and 50% RH) the air flow
through the close control unit is 0.8 m3/s. And I dont have anymore
information.
One other question; is there any kind of curves required in the
COIL:DX:coolingBypassFactorEmpirical that could be used in a standard way?
Because I dont have any information about the coil performance.
Thank you very much, Emanuel
----- Original Message -----
From: "Michael J. Witte" <mjwitte@xxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Tuesday, October 04, 2005 5:23 PM
Subject: Re: [EnergyPlus_Support] air flow limit
> The DX coil model warns when the airflow rate to capacity ratio is outside
> the
> typical range, because this may impact the results. If the airlfow is
> only a
> little out of range, the results are probably acceptable. What type of
> equipment is this? The reported airflow rate is higher than the upper
> limit on
> the warning check, so this system will not dehumidify very well. For the
> DX
> coil capacity, check to see if the catalog data is the gross coil capacity
> or
> the net capacity (including the heating effect of the fan). The DX coil
> input
> should be the gross capacity, which for cooling is the larger of the two
> values.
>
> Mike
>
>
> On 3 Oct 2005, at 1:25, dust_broom wrote:
>
>> Dear all:
>>
>> During the simulation this error came up, but I dont understand the
>> purpose!
>>
>> ** Severe ** Sizing: COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "COIL
>> SISTEMA UNDERFLOW": Rated air volume flow rate per watt of rated
>> total cooling capacity is out of range. See Input-Output Reference
>> Manual for valid range.
>> ** Warning ** COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "COIL SISTEMA
>> UNDERFLOW" - Air volume flow rate per watt of rated total cooling
>> capacity is out of range at 7.120244238500870E-005 m3/s/w.
>> ** ~~~ ** ...VolumeFlowperRatedTotCap=7.120E-005 Occurrence
>> info=SUMMER DESIGN DAY IN TITLE, 07/21 01:00 - 02:00
>> ** ~~~ ** Expected range for VolumeFlowperRatedTotalCapacity=
>> [ 3.356000000000000E-005-- 6.713000000000000E-005]
>> ** ~~~ ** Possible causes include inconsistent air flow rates
>> in system components,
>> ** ~~~ ** inconsistent supply air fan operation modes in coil
>> and furnace/unitary objects,
>> ** ~~~ ** or variable air volume [VAV] system using incorrect
>> coil type.
>>
>>
>>
>>
>> The air flow used in this simulation was took from the catalog, so
>> I should not change it. I would like to know if there is any way to
>> avoid this error without changing the flow rate, or if I keep the
>> air flow rate, will this result in substancial errors?
>>
>> Thank you, Emanuel
>>
>>
>>
>>
>>
>>
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the appropriate
>> folder
>> in the Files area of the Support Web Site.
>>
>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
>> the
>> "search" button.
>>
>> Yahoo! Groups Links
>>
>>
>>
>>
>>
>>
>>
>>
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/