Re: [EnergyPlus_Support] air flow limit
I got the cooling capacity from the same catalog. Thats why I dont know how
to solve the problem!
Emanuel
----- Original Message -----
From: "Michael J. Witte" <mjwitte@xxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Tuesday, October 04, 2005 9:33 PM
Subject: Re: [EnergyPlus_Support] air flow limit
Where did you get the cooling capacity from?
The curves in any of the DX coil example files can be used as generic
curves.
Mike
On 4 Oct 2005, at 17:45, Emanuel Sá wrote:
> This is a Close control equipment that provides a unferfloor flow. the
> catalog says that for standard conditions (24ºC and 50% RH) the air flow
> through the close control unit is 0.8 m3/s. And I dont have anymore
> information.
> One other question; is there any kind of curves required in the
> COIL:DX:coolingBypassFactorEmpirical that could be used in a standard way?
> Because I dont have any information about the coil performance.
>
> Thank you very much, Emanuel
>
> ----- Original Message -----
> From: "Michael J. Witte" <mjwitte@xxxxxxxx>
> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Tuesday, October 04, 2005 5:23 PM
> Subject: Re: [EnergyPlus_Support] air flow limit
>
>
> > The DX coil model warns when the airflow rate to capacity ratio is
> > outside the
> > typical range, because this may impact the results. If the airlfow is
> > only a
> > little out of range, the results are probably acceptable. What type of
> > equipment is this? The reported airflow rate is higher than the upper
> > limit
> > on the warning check, so this system will not dehumidify very well. For
> > the
> > DX coil capacity, check to see if the catalog data is the gross coil
> > capacity
> > or the net capacity (including the heating effect of the fan). The DX
> > coil
> > input should be the gross capacity, which for cooling is the larger of
> > the two
> > values.
> >
> > Mike
> >
> >
> > On 3 Oct 2005, at 1:25, dust_broom wrote:
> >
> >> Dear all:
> >>
> >> During the simulation this error came up, but I dont understand the
> >> purpose!
> >>
> >> ** Severe ** Sizing: COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "COIL
> >> SISTEMA UNDERFLOW": Rated air volume flow rate per watt of rated
> >> total cooling capacity is out of range. See Input-Output Reference
> >> Manual for valid range.
> >> ** Warning ** COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "COIL SISTEMA
> >> UNDERFLOW" - Air volume flow rate per watt of rated total cooling
> >> capacity is out of range at 7.120244238500870E-005 m3/s/w.
> >> ** ~~~ ** ...VolumeFlowperRatedTotCap=7.120E-005 Occurrence
> >> info=SUMMER DESIGN DAY IN TITLE, 07/21 01:00 - 02:00
> >> ** ~~~ ** Expected range for VolumeFlowperRatedTotalCapacity=
> >> [ 3.356000000000000E-005-- 6.713000000000000E-005]
> >> ** ~~~ ** Possible causes include inconsistent air flow rates
> >> in system components,
> >> ** ~~~ ** inconsistent supply air fan operation modes in coil
> >> and furnace/unitary objects,
> >> ** ~~~ ** or variable air volume [VAV] system using incorrect
> >> coil type.
> >>
> >>
> >>
> >>
> >> The air flow used in this simulation was took from the catalog, so
> >> I should not change it. I would like to know if there is any way to
> >> avoid this error without changing the flow rate, or if I keep the
> >> air flow rate, will this result in substancial errors?
> >>
> >> Thank you, Emanuel
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >> The primary EnergyPlus web site is found at:
> >> http://www.energyplus.gov
> >>
> >> The group web site is:
> >> http://groups.yahoo.com/group/EnergyPlus_Support/
> >>
> >> Attachments are not allowed -- please post any files to the appropriate
> >> folder in the Files area of the Support Web Site.
> >>
> >> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> >> press the
> >> "search" button.
> >>
> >> Yahoo! Groups Links
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> > press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
Yahoo! Groups Links
------------------------ Yahoo! Groups Sponsor --------------------~-->
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/