RE: [EnergyPlus_Support] Surface Heat Balance of Decoupled PV
Hello,
Yes, shading effects are considered. The incident solar will be reduced if other surfaces in the model will shade the PV panels.
If by "decoupled" you mean you are using the object "Surface:HeatTransfer:ExteriorNaturalVentedCavity" then the model assumes that none of the solar will make it to the underlying surface, it is all incident on the decoupled surface (baffle) that has the panels.
No, you do not include the PV panel in the construction of the base surface. (But if you were modeling PV as "integrated", then you would include it in the construction, but you would use a "Construction With Internal Source" object.)
Brent
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of wah
Sent: Thursday, October 06, 2005 8:30 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Surface Heat Balance of Decoupled PV
Dear all,
For the case of decoupled PV, does the surface heat balance consider the shading effect
by the PV panels? If a PV is input as decoupled, do we need to include it in the construction
of the base surface?
Thank you!
PuiWah
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
_____
YAHOO! GROUPS LINKS
* Visit your group " EnergyPlus_Support <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
* To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
* Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> .
_____
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/