Thank you,Brent/(Fred), for your elaborated explaination. So can I 
assume that the "normalization" means a ratio of a real-condition 
parameter to a rated-point one? Then how about curves of Electric 
Chiller, WindAC,Direct-fired absorption Chiller? Are they called 
normalized curves?

John

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent" 
<brent_griffith@n...> wrote:
>
> John, 
>  
> Keep in mind that there are at least two possible "policies" for 
curve-fits.  One option is to use curves that are normalized with 
respect to capacity (or efficiency) at a single operating point.  
The other is to use curves that directly fit the capacity/efficiency 
data without normalization.   It is not unreasonable practice to use 
normalized curves for components that have a different nominal 
capacity or efficiency than the one used to produce the curves.  
Clearly it is better to use performance curves that apply to the 
unit being modeled, but this isn't always practical.  On the other 
hand, direct performance curves (that aren't normalized) are 
basically limited to the original unit and cannot be used to model 
components with a different size or nominal performance.  
>  
> Developers have different opinions on which is the best way to 
go.  The normalized-curve group want curves to be more general so 
that one can easily adjust equipment capacities when doing a 
simulation study.  The direct-curve group are more leary of the 
pitfalls of abusing curves and want to force the user to use curves 
that match the component.  I am not sure if it is true across the 
board, but curves tend to be of the normalized type in EnergyPlus.  
So it is not blatently wrong to reuse such curves for different 
capacities.  However, do not assume that the example files that ship 
with EnergyPlus represent best modeling practice. It is better to 
think of them as test and demonstration files.       
>  
> Brent 
> 
>  -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx 
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of 
deserteagle_zhou
> Sent: Tuesday, October 11, 2005 4:13 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] validation of extensive coefficients 
use
> 
> 
> 
> Hi,there,
> 
> Components, i.e., chiller, fan, etc, are defined according to a 
> performance curve-fit policy. Curves, however, often have 
something to 
> do with the real working conditions and an equipment capacity. I 
think 
> users are not supposed to use directly the same coefficients as 
before 
> after the equipment capacity has been changed. That means we 'd 
better 
> not use directly the curves and parameters in E+ example files 
directly 
> unless we cannot get the data from the equipment producer.
> Is this understanding right or not?
> 
> Another question is whether the object SINGLE DUCT:VAV REHEAT can 
deal 
> with heating condition alone in a zone without a company heating 
device 
> (such as a baseboard heater), especially in a cold area? 
> 
> Thank you. 
> John
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the 
appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
and press the "search" button.
> 
> 
> 
> 
>   _____  
> 
> YAHOO! GROUPS LINKS 
> 
> 
> 	
> *	 Visit your group " EnergyPlus_Support 
<http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
>   
> 
> *	 To unsubscribe from this group, send an email to:
>   EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
<mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
subject=Unsubscribe> 
>   
> 
> *	 Your use of Yahoo! Groups is subject to the Yahoo! Terms 
of Service <http://docs.yahoo.com/info/terms/> . 
> 
> 
>   _____  
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
>






------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/