Dear Mike,
sorry for the deleted response. The problem I described (Free
cooling heat exchanger: hydronic) was not fixed.
I controlled my inputs another time and I didn't found any errors
like node connection errors or branch errors.
After a few tests, I could point out the main problem: When I use
two heat exchangers: hydronic: Free cooling- objects, the simulation
crashed, because the calculated inlet mass flow rate for demand side
splitter doesn't match with the outlet mass flow rate of the demand
side splitter.
Furthermore the mass flow rate for the demand side splitter inlet
calculated by energy plus was always the double of the mass flow
rate on the demand side mixer outlet, which is the same mass flow
rate as for the supply side splitter inlet.
It seems that there is a mass flow source somewhere in the supply
side of the cooling loop, but this couldn't be (I could not
understand where and why).
After this I started a simulation where only one of the condenser
loops was connected with the cooling loop by a chiller and a heat
exchanger: hydronic: Free cooling- object and the other condenser
loop by a normal chiller.
The simulation didn't crash.
The resultant questions are:
1. How many heat exchanger: hydronic: Free cooling- objects are
allowed for each cooling loop
2. Is there a controller for the mass flow rates or the load
distribution for the heat exchanger: hydronic: Free cooling- object,
because it could be that there are some problems with the load /
mass flow distribution, when I use more then one free cooling object?
I have seen, that you asked if I have a bypass on the demand side of
the cooling loop.
Yes there is a bypass on the demand side. I've tried a simulation
without the bypass on the demand side, but the simulation crashed
too.
I will upload the file to the file area for the case that you will
have a look at it.
Attachments:
Heat_exchanger_free_cooling.zip
Best regards,
Patrik
------------------------ Yahoo! Groups Sponsor --------------------~-->
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/