Re: [EnergyPlus_Support] zone set point with deadband
EnergyPlus Thermostats do not support a throttling range within the cooling or
heating mode. They only support a deadband in which the zone has no heating or
cooling load. The best you can do is to cool to 23C. There is no way to
specify +/- 1C. You are correct that you need a controller:simple, setpoint
manager:single zone cooling, and a zone control:thermostatic. The thermostat
should use the single cooling setpoint control type.
Mike
On 17 Nov 2005, at 16:34, Clarice Bleil de Souza wrote:
> Hi everybody,
>
> I am trying to simulate a zone thermostat with 23deg -1deg, + 1deg.for cooling
> only, as it is in a hot weather. I want this temperatre to be controlled by a
> variable flow in my cooling coil system.
>
> To do this I suppose I need to define a "controller:simple" and set the ctrl
> variable to the outlet air temperature of the coil and the actuated variable to
> the water flow rate through coil. Then I suppose I need to specify the "setpoint
> manager" as "single zone cooling" and set the name of the node where the
> temperature is going to be set as the cooling coil outlet. Finally, I suppose I
> need to specify a setpoint for the zone which I can do in the zone control and
> thermostats. But the thing is the only way to specify a deadband in this group
> is by setting dual setpoint with a deadband, which would allow me to use a
> schedule with 22deg as the lower band and 24deg as the upper one simulating the
> effect of 23deg, -1deg, +1deg.
>
> Can I use this setpoint together with a cooling only system? Or do I need to
> specify a whole heating system and set all it's parameteres to zero? Is there
> any other way to specify a setpoint with a deadband for the zone?
>
> I thank you very much for your attention and hope hearing from you soon
>
> Regards,
>
> Clarice
>
>
> ---------------------------------
> Yahoo! Acesso Grátis: Internet rápida e grátis.
> Instale o discador agora!
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get fast access to your favorite Yahoo! Groups. Make Yahoo! your home page
http://us.click.yahoo.com/dpRU5A/wUILAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/