Re: [EnergyPlus_Support] Set point not met
Hi
Thanks, that worked just fine!!
I have one other problem.
In this building that i'm simulating, there are high internal gains, so it
requires cooling all year. It also requires humidity control so I instaled a
terminal reheat coil and a boiler.
In the design file (eio) says that the design hot water flow is " Design
Boiler Water Flow Rate [m3/s], 0.31956E-02" which is 3.1956 kg/s aprox.
however, in the spreadsheet I see that the demand bypass flow is never less
than 3.17 kg/s !!! so, I dont understand how this design flow rate is
possible! the gas consuming is almost equal to the chiller electric
consuming!!
Am'I doing anything wrong?
Thank you very much!
----- Original Message -----
From: "Michael J. Witte" <mjwitte@xxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, November 23, 2005 9:26 PM
Subject: Re: [EnergyPlus_Support] Set point not met
> Yes, a properly autosized system should be able to meet the zone setpoints
> on
> the design days. Things to check:
>
> 1. If using coil:water:cooling, we have recently learned that it may not
> size
> properly if the design delta humidity ratio is less than 0.01. Check the
> component sizing report for the cooling coil(s) in the eio output file.
> If the
> design entering minus leaving humidity ratio is smaller than 0.01, change
> to
> using the COIL:Water:DetailedFlatCooling
>
> 2. Is the supply air temperature setpoint being met? The design supply
> air
> temperatures in the sizing objects must match the setpoint controls in the
> simulation.
>
> 3. Are the chillled water/hot water supply setpoints being met? Again,
> the
> setpoint controls must match the specifications in the plant sizing
> objects.
>
> 4. Also check availability schedules.
>
> Mike
>
>
> On 23 Nov 2005, at 5:07, dust_broom wrote:
>
>> Dear all.
>>
>> I've simulated a cooling system for a 4 zone bilding using a chiller a
>> boiler(for reheat), coils and a single duct . Every component was
>> suposed to be autosized. So I did the autosize. But than, in the
>> results I saw that only one of the four zones had its temperature
>> correct. the others were floating arround 6 degrees. Even in the
>> design day simulation some zones were too hot. shouldn't the design
>> day be sizing those equipments in order to maintain the zone
>> temperatura as specified? Am I doing anything wrong?
>>
>> Thank you, Emanuel
>>
>>
>>
>>
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the appropriate
>> folder
>> in the Files area of the Support Web Site.
>>
>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
>> the
>> "search" button.
>>
>> Yahoo! Groups Links
>>
>>
>>
>>
>>
>>
>>
>>
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get fast access to your favorite Yahoo! Groups. Make Yahoo! your home page
http://us.click.yahoo.com/dpRU5A/wUILAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/