 If the two zones have similar temperature controls, it may be reasonable to 
ignore these openings.

For convective transfer between zones, use MIXING or CROSS MIXING for a simple 
model or use the COMIS airflow objects for a detailed model, but read carefully 
the limitations of COMIS regarding large horizontal openings.

For solar radiation to pass from one zone to another requires the use of a 
window subsurface.

(See also similar topic originally posted on 24 Jan 2006 and replies.)

Mike


On 1 Feb 2006 at 10:05, simoboninsegna wrote:

> Hello to all,
> 
> how have I to define a hole in the ceiling between two zones of the 
> building? The hole I want to model (for example the stairshole) must be 
> just a void in the ceiling of the room on floor downstair. The hole 
> should termally affects the climate of the 2 rooms only by convection 
> and irradiation. 
> 
> Thank you 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/