RE: [EnergyPlus_Support] double skin



There is an EnergyPlus example file "PurchAirWithDoubleFacadeDaylighting.idf" 
which models the double-facade as a separate thermal zone.  EnergyPlus also has 
airflow windows which are another approach to modeling a double-skin, 
"AirflowWindowsAndBetweenGlassBlinds.idf".  The best approach depends on the 
specifics of the double-skin design.  With either approach, it is important to 
recognize that there are many inputs which will be difficult to quantify.  It 
is best to perform a range of simulations, including an option with a single-
skin facade to be sure that results are reasonable.

Mike


On 27 Feb 2006 at 10:27, Ian Doebber wrote:

> Check out the following site:
>  
> Dr. Karl Gertis (director of the Fraunhofer Institute of Building Physics in
> Stuttgart, Germany) provides a critical review of double-skin façades in one
> of his article and cites some problems in the literature regarding research
> related to Glass Double Facade 
> 
>  
> 
> For more information about the article please go to the following link:
> 
>  
> 
> http://gaia.lbl.gov/hpbf/perfor_c.htm
> <BLOCKED::http://gaia.lbl.gov/hpbf/perfor_c.htm> 
> 
>  
> Ian Doebber
> Graduate Mechanical Engineer
> Arup
> 901 Market Street Suite 260 San Francisco CA 94103
> tel: 415-946-0292
> fax: 415-957-9096
> cell: 415-613-4314
> ian.doebber@xxxxxxxx
> www.arup.com
>  
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of ???
> Sent: Sunday, February 26, 2006 6:20 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] double skin
> 
> 
> hi anyone
>    
>   i'm studying about double skin 
>    
>   are there examples about double skin ? 
>    
>   is it exist please give me that kind of thing? 
>    
>   if you do that i really appreciate it 
>    
>   thanks any way
> 
>                         
> ---------------------------------
> 
> ! 
>  1GB !,     ! 
> .
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> 
> 
> 
> 
> SPONSORED LINKS 
> Medical software program
> <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Medical+softw
> are+program&w2=Email+software+program&w3=Maintenance+program+software&w4=Weddi
> ng+program+software&w5=Cad+software+program&w6=Backup+software+program&c=6&s=1
> 77&.sig=thfNN9EZNNHCqvCT17zHrw>  	Email software program
> <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Medical+softwar
> e+program&w2=Email+software+program&w3=Maintenance+program+software&w4=Wedding
> +program+software&w5=Cad+software+program&w6=Backup+software+program&c=6&s=177
> &.sig=06IwiVFwBunuqaglp3BOgA>  	Maintenance program software
> <http://groups.yahoo.com/gads?t=ms&k=Maintenance+program+software&w1=Medical+s
> oftware+program&w2=Email+software+program&w3=Maintenance+program+software&w4=W
> edding+program+software&w5=Cad+software+program&w6=Backup+software+program&c=6
> &s=177&.sig=CXP-CG7bvxdq6KQvxUCLGw>  	
> Wedding program software
> <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Medical+softw
> are+program&w2=Email+software+program&w3=Maintenance+program+software&w4=Weddi
> ng+program+software&w5=Cad+software+program&w6=Backup+software+program&c=6&s=1
> 77&.sig=vaTGBEgrBbXBJwMD2bC1rw>  	Cad software program
> <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Medical+software+
> program&w2=Email+software+program&w3=Maintenance+program+software&w4=Wedding+p
> rogram+software&w5=Cad+software+program&w6=Backup+software+program&c=6&s=177&.
> sig=xZ6VbO5TgEy-LWMsCycm8A>  	Backup software program
> <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Medical+softwa
> re+program&w2=Email+software+program&w3=Maintenance+program+software&w4=Weddin
> g+program+software&w5=Cad+software+program&w6=Backup+software+program&c=6&s=17
> 7&.sig=ZXnsAqU9P5Lgaq5PVU3GFQ>  	
> 
> ________________________________
> 
> YAHOO! GROUPS LINKS 
> 
> 
> 	
> *	 Visit your group "EnergyPlus_Support
> <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
> 	  
> *	 To unsubscribe from this group, send an email to:
> 	 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> 
> 	  
> *	 Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
> <http://docs.yahoo.com/info/terms/> . 
> 
> 
> ________________________________
> 
> 
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup  business
> systems are scanned for acceptability of content and viruses
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/