[EnergyPlus_Support] Re: Control Node Setup
Thanks for all the help.
John.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> Since you have 2 reheat coils, I assume that they are part of a
terminal unit
> such as SINGLE DUCT:CONST VOLUME:REHEAT or SINGLE
DUCT:VAV:REHEAT. These
> components have the reheat controls built into the terminal unit
and do not
> require a set point manager or a CONTROLLER:SIMPLE object. SET
POINT
> MANAGER:SINGLE ZONE REHEAT is used to control coils in the main
branch of an
> air loop, not in terminal units.
>
> To control dehumidification, the cooling coil requires both a
temperature set
> point manager and a Set Point Manager:Single Zone Max Hum (as
mentioned below)
> to override when humidity control is required.
>
> If this system is serving 2 zones, SET POINT MANAGER:SINGLE ZONE
COOLING will
> not work, because it will control the cooling coil for only the
single zone it
> is attached to. SET POINT MANAGER:WARMEST may be better for this
application.
>
> Mike
>
>
> On 28 Feb 2006 at 11:27, Richard Raustad wrote:
>
> > Try using the Set Point Manager:Single Zone Max Hum as the set
point
> > manager for the cooling coil. Use a Humidistat in one zone to
control
> > the steam humidifier at some minimum zone humidity set point and
a
> > humidistat in the other zone to control the cooling coil to some
maximum
> > zone humidity set point. You will also need to specify
TEMPandHUMRAT as
> > the control variable for the CONTROLLER:SIMPLE used for the
cooling
> > coil. You should also be using a Set Point Manager:Single Zone
Min Hum
> > with the steam humidifier.
> >
> > civilnug wrote:
> >
> > > Hi All,
> > >
> > > I have a fixed flow system feeding two zones, on the air loop
there's
> > > a cooling coil and a supply fan followed by a steam
humidifier, I then
> > > have two separate reheat coils serving the two zones. In these
zones I
> > > want to control both the temperature and the humidity.
> > >
> > > I have a CONTROLLER:SIMPLE for each of the coils (1 cooling, 2
> > > reheats) and SET POINT MANAGER:SINGLE ZONE REHEAT for the
reheats and
> > > SET POINT MANAGER:SINGLE ZONE COOLING for the cooling coil.
> > >
> > > I'm able to get control of the RH or the temperature in the
zones but
> > > not both at the same time.
> > >
> > > Could my control nodes be the source of the problem?
> > >
> > > Regards,
> > > John.
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> > > appropriate folder in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open
EPlusMainMenu.idf and
> > > press the "search" button.
> > >
> > >
> > >
> > >
> > > SPONSORED LINKS
> > > Backup software program
> > >
> > <http://groups.yahoo.com/gads?
t=ms&k=Backup+software+program&w1=Backup+softwar
> >
e+program&w2=Maintenance+program+software&w3=Email+software+program&w
4=Wedding
> >
+program+software&w5=Cad+software+program&w6=Medical+software+program
&c=6&s=17
> > 7&.sig=28qN3sGcwWF911j7OnqOxg>
> > > Maintenance program software
> > >
> > <http://groups.yahoo.com/gads?
t=ms&k=Maintenance+program+software&w1=Backup+so
> >
ftware+program&w2=Maintenance+program+software&w3=Email+software+prog
ram&w4=We
> >
dding+program+software&w5=Cad+software+program&w6=Medical+software+pr
ogram&c=6
> > &s=177&.sig=1FZNh98D0Ht8QnMNfbG3TQ>
> > > Email software program
> > >
> > <http://groups.yahoo.com/gads?
t=ms&k=Email+software+program&w1=Backup+software
> >
+program&w2=Maintenance+program+software&w3=Email+software+program&w4
=Wedding+
> >
program+software&w5=Cad+software+program&w6=Medical+software+program&
c=6&s=177
> > &.sig=pD1X5O_PBt00SkIKrscENA>
> > >
> > > Wedding program software
> > >
> > <http://groups.yahoo.com/gads?
t=ms&k=Wedding+program+software&w1=Backup+softwa
> >
re+program&w2=Maintenance+program+software&w3=Email+software+program&
w4=Weddin
> >
g+program+software&w5=Cad+software+program&w6=Medical+software+progra
m&c=6&s=1
> > 77&.sig=x6S7GFcuBa1Sq4_ZqCZ0Og>
> > > Cad software program
> > >
> > <http://groups.yahoo.com/gads?
t=ms&k=Cad+software+program&w1=Backup+software+p
> >
rogram&w2=Maintenance+program+software&w3=Email+software+program&w4=W
edding+pr
> >
ogram+software&w5=Cad+software+program&w6=Medical+software+program&c=
6&s=177&.
> > sig=wjmBspWizYl54SWucSUuxg>
> > > Medical software program
> > >
> > <http://groups.yahoo.com/gads?
t=ms&k=Medical+software+program&w1=Backup+softwa
> >
re+program&w2=Maintenance+program+software&w3=Email+software+program&
w4=Weddin
> >
g+program+software&w5=Cad+software+program&w6=Medical+software+progra
m&c=6&s=1
> > 77&.sig=0a7BUpUe9NvS9Yit40hqPA>
> > >
> > >
> > >
> > > ---------------------------------------------------------------
---------
> > > YAHOO! GROUPS LINKS
> > >
> > > * Visit your group "EnergyPlus_Support
> > > <http://groups.yahoo.com/group/EnergyPlus_Support>" on
the web.
> > >
> > > * To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
subject=Unsubscribe>
> > >
> > > * Your use of Yahoo! Groups is subject to the Yahoo!
Terms of
> > > Service <http://docs.yahoo.com/info/terms/>.
> > >
> > >
> > > ---------------------------------------------------------------
---------
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/