This usually means that the tower model is being asked to do something
impossible. It could mean inconsistent temperature inputs or a bad flow rate.
Check the sizing output results in the eio file for components leading up to
the tower, such as the chiller condenser water flow rate. Also check the plant
sizing temperatures for the condenser loop against the design day conditions.
Mike
On 13 Mar 2006 at 15:30, tonybaxterhevacomp wrote:
> Hello anyone,
>
> I am using a water cooled chiller, with a cooling tower.
> I get the error :
>
> ** Severe ** Bad starting values for UA
> ** Fatal ** Autosizing of cooling tower UA failed for tower PLANT1
>
> I have a Cooling tower and a Condenser loop, using autosizing
> wherever possible:
>
> CONDENSER LOOP,Loop,Water,LoopOp,AIR,80,5,autosize,0.0,autosize,
> Pin,Pout,Blist,Clist,DemandIn,DemandOut,DBlist,DClist,Sequential;
>
> COOLING TOWER:SINGLE SPEED,Plant1,PlantIn,PlantOut,
> autosize,autosize,autosize,autosize,0.0,0.0;
>
> PLANT SIZING,Loop,Condenser, 23 , 5 ;
>
> Could anyone help me please?
>
> Tony Baxter
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/