Re: [EnergyPlus_Support] Extract ventilation





tonybaxterhevacomp wrote:

>Hello anyone,
>
>I wish to simulate a building with an extract ventilation system only, 
>no supply air.  I have done this initially using ZONE EXHAUST FAN 
>objects for each zone.
>
>Now I want to have a duct system connecting multiple zones, with a 
>single extract fan.  Can I set up an AIR PRIMARY LOOP without any 
>supply ?
>  
>
No; every AIR PRIMARY LOOP is a loop, with return air, outside air, 
mixed air, supply air.
Also, the air flow must be balanced. Thus whenever you exhaust air, this 
must be balanced by
inlet outside air which is part of the supply air. So to use an AIR 
PRIMARY LOOP, you would need
to set up the usual air loop but ensure there is no return air by 
setting the min outside air flow rate
to the maximum in the OA Controller object.

Fred Buhl

>Any help would be appreciated.
>
>Tony
>Hevacomp
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>
>  
>


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/