RE: R: [EnergyPlus_Support] Vented Facade
Hi,
The baffle will get all the sun and completely shade the underlying surface.
There is no need to use "construction with internal source” or “surface:shading:detached:fixed" for this model (but you could if there were other reasons to do so).
Emanuele, I don't necessarily see a problem with the temperatures you describe below. The cavity air temperature can be expected to be lower than two surfaces because of air exchanges with cooler exterior ambient. The underlying surface's outside face is also exchanging long wave radiation with the hot baffle. So it can get hotter than the cavity air, but this energy isn't from the sun. Your numbers indicate that radiation heat transfer rate is about twice the convection heat transfer rate, which seems reasonable at these temperatures. You should also look at an entire day's worth of data on the outside face surface temperature. Because of the transient heat transfer and capacity effects in the underlying surface, it is easy to get missled by data for a single point in time.
Brent
> -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of fred buhl
> Sent: Friday, March 24, 2006 10:51 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: R: [EnergyPlus_Support] Vented Facade
>
>
> Emanuele,
>
> You probably need to add a shade. The baffle may not automatically
> generate one.
> Brent probably knows if it does.
>
> Fred
>
> Emanuele Naboni wrote:
>
> >Brent,
> >
> >
> >
> >In the specific case I’m simulating a simple external
> surface with thin
> >ceramic and with a gap of 3 inches, that is suppose of
> generate chimney
> >effects.
> >
> >The not realistic thing is that the temperature of the
> baffle (ceramic) for
> >example in 21 July at 12 is 80°C, the cavity is 50° and the
> outside face of
> >the support wall is around 70°C. It seems that the buffle’
> protection from
> >the sun isn’t calculated.
> >
> >
> >
> >I was wondering if I have to set any parameters in “construction with
> >internal source” or maybe describe the ceramic external layer in
> >“surface:shading:detached:fixed”
> >
> >Thank you very much.
> >
> >
> >
> >Emanuele,
> >
> >Which surface temperatures of the support wall are you
> refering to? inside
> >or outside? Check what you have set for
> OutsideFaceEnvironment -- it
> >should be OtherSideConditionsModel
> >
> >Brent
> >
> >
> >
> >-----Original Message-----
> >From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of
> Emanuele Naboni
> >Sent: Wednesday, March 15, 2006 11:35 AM
> >To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >Subject: Re: [EnergyPlus_Support] Vented Facade
> >
> >
> >Hi everybody,
> >
> >I'm simulting as well an opaque ventilated facade, It works and is
> >very intersting!
> >The baffle and the cavity have very realistic values.
> >
> >The only problem is about the effects it does on the wall
> where is applied:
> >running a simulation with a vent facade and running another one
> >without vent facade gives the same temperatures on the support wall.
> >have anyone verify that?
> >
> >I'm very intersted too in the Cd values.
> >Emanuele
> >
> >
> >
> >
> >
> >[Non-text portions of this message have been removed]
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the
> appropriate
> >folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable. Open
> EPlusMainMenu.idf and press
> >the "search" button.
> >
> >
> >
> >
> >SPONSORED LINKS
> >
> >
> >Wedding
> ><http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software
> &w1=Wedding+pro
> >gram+software&w2=Medical+software+program&w3=Cad+software+pro
> gram&w4=Backup+
> >software+program&w5=Anti+virus+software+program&c=5&s=148&.si
g=A878GW0g_8cK_
> >-3yeacaXw> program software
> >
> >Medical
> ><http://groups.yahoo.com/gads?t=ms&k=Medical+software+program
> &w1=Wedding+pro
> >gram+software&w2=Medical+software+program&w3=Cad+software+pro
> gram&w4=Backup+
> >software+program&w5=Anti+virus+software+program&c=5&s=148&.si
> g=4nf2B8B2-yd_x
> >IZXEGy56g> software program
> >
> >Cad
> ><http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=
> Wedding+program
> >+software&w2=Medical+software+program&w3=Cad+software+program
> &w4=Backup+soft
> >ware+program&w5=Anti+virus+software+program&c=5&s=148&.sig=-J
> lMDVZyj77LC5mzp
> >xMvmg> software program
> >
> >
> >Backup
> ><http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&
> w1=Wedding+prog
> >ram+software&w2=Medical+software+program&w3=Cad+software+prog
> ram&w4=Backup+s
> >oftware+program&w5=Anti+virus+software+program&c=5&s=148&.sig
=lt4Re674q4yJSq
> >sb7xllEA> software program
> >
> >Anti
> ><http://groups.yahoo.com/gads?t=ms&k=Anti+virus+software+prog
> ram&w1=Wedding+
> >program+software&w2=Medical+software+program&w3=Cad+software+
program&w4=Back
> >up+software+program&w5=Anti+virus+software+program&c=5&s=148&
.sig=p8dQegVsv1
> >kjnWftX3TU-Q> virus software program
> >
> >
> >
> >
> >
> > _____
> >
> >YAHOO! GROUPS LINKS
> >
> >
> >
> >* Visit your group "EnergyPlus_Support
> ><http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
> >
> >* To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> ><mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subjec
> t=Unsubscribe>
> >
> >* Your use of Yahoo! Groups is subject to the Yahoo!
> ><http://docs.yahoo.com/info/terms/> Terms of Service.
> >
> >
> >
> > _____
> >
> >
> >
> >[Non-text portions of this message have been removed]
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable. Open
> EPlusMainMenu.idf and press the "search" button.
> >
> >Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open
> EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/