Re: [EnergyPlus_Support] Outside air problem



This should work.  In CONTROLLER:OUTSIDE AIR, specify the desired outside air 
flow rate for "minimum outside air flow rate".  This will be the outside air 
flow rate when the VAV system is at full flow.  If you want this to remain 
fixed, even when the VAV system flow is reduced, then set MinimumLimit to FIXED 
MINIMUM.  One exception is if the VAV system flow is reduced below the 
specified "minimum outside air flow rate", the outside air flow will be reduced 
to provide 100% outside air at whatever the system flow rate is for that time.

Mike


On 24 Mar 2006 at 12:09, dust_broom wrote:

> Hi!
> 
> I am using the EnergyPlus to install a VAV system in a building with 
> several zones and I need to fix my outside air flow value. I tried to 
> do 
> it in the Controller:Outside Air function but it doesn't work. The 
> outside air value is always the autosized one (In all other components 
> the airflow values are autosized).
> Does any one know how to solve my problem?
> 
> Thanks
> Petra
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/