[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] U-values in E+
As you know, the surface details report (report, surfaces, details;) gives U-
values with and without film coefficients. The construction report (report,
construction;) reports a thermal conductance without film coefficients, which
should be the same value as the "Nominal U (w/o film coefs)".
For the "Nominal U (with film coefs)", there is a table of film coefficients
given in the "Output Details and Examples" document, p. 26 (pdf p. 32). I see
that this table is in I-P units. Here are the values in S-I units (which we
will add to the document, but it might be too late to add for the 1.3 release).
These values are directly from the source code:
Surface type, Interior film, Exterior film {m2-K/W}
Wall, 0.1197548 , 0.0299387
Floor, 0.1620212 , 0.0810106
Ceiling/Roof, 0.1074271 , 0.0810106
Would you please repeat your hand calculations using the above values and
confirm if this agrees with the reported "Nominal U (with film coefs)"?
Mike
On 20 Apr 2006 at 13:03, Clarice Bleil de Souza wrote:
> Hi Everybody,
>
> I am trying to run some simulations with different U-values to check the
> sensitivity of the results and I was wondering, how does E+ calculates the
> U-values.
> I have some material compositions that gives me 0.5w/m2K calculated by hand
> (using Rso = 0.055 and Rsi = 0.123 - using the inverse sum of the
> resistivities in series) and E+ gives me 0.55 which is near. Once I look for a
> more conductive material with a hand calculated value of 3 w/m2K, Energy Plus
> gives me a value of 6.5W/m2K. I could not understand why this is happenning. I
> know the U-values won't be used by E+ but I want to be sure that results will
> be somehow equivalent. Can you please let me know how E+ calculates the
> U-values? I couldn't find anything about it in the documentation.
>
> Thanks a lot for your attention and hope hearing from you soon,
>
> Regards,
>
> Clarice
>
>
>
>
> ---------------------------------
> Abra sua conta no Yahoo! Mail - 1GB de espaço, alertas de e-mail no celular e
> anti-spam realmente eficaz.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/