[EnergyPlus_Support] mixing autosized and manual input for a BASEBOARD HEATER:Water:Convective object
Hello all,
I have a question pertaining to autosizing BASEBOARD
HEATER:Water:Convective objects.
In the simulation model, the BASEBOARD HEATER:Water:Convective
objects are the only energy tempering devices in the room.
Simulation Run 1: Set the UA from UA = q(loss) / (t(water)-t(air))
and autosize water flow rate
If I run the simulation and concentrate on one particular zone, the
heating design load is 718.55 W. Assuming the room temp is 20C and
the water temp is 80C, this would leave a UA of 11.98 W/dK. However,
if you use this values in the input configuration for UA: (1) the
zone temperature is not consistently maintained at 20C and (2) the
maximum load from the heater is never greater than 360.81 W.
Simulation Run 2: Autosize the UA and water flow rate
EnergyPlus calculates the values of UA to be 18.933. The zonal
conditions are spot on. The only odd behaviour is that the max
output from the heater is never greater than 600 W.
Simulation Run 3: Set the UA from the last run and water flow rate
Now the zonal conditions are not maintained even though nothing was
changed except manually configuring the UA syntax to the autosized
value from the previous run.
Can anyone explain this?
Kind regards
-Elmer
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/