[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Autosizing air and water circuits for zone heating
Can anyone help?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Elmer Morrissey"
<elmofuddly@...> wrote:
>
> Hello all,
>
> I have another autoszing problem. I have 3 zones that are fed with
> heated auxiliary air at 20C supply air. Any additional heat
required
> to maintain zone temps should be picked up by convector units.
>
> ZONE EQUIPMENT LIST,
> Equip:1, !- Name
> DIRECT AIR, !- KEY--Zone Equipment Type 1
> RB:1, !- Type Name 1
> 1, !- Cooling Priority 1
> 1, !- Heating Priority 1
> BASEBOARD HEATER:WATER:CONVECTIVE, !- KEY--Zone Equipment
Type 2
> HB:1, !- Type Name 2
> 2, !- Cooling Priority 2
> 2; !- Heating Priority 2
>
> A boiler system supplies hot water to the heating coil in the AHU
> and to the convector units.
>
> (from my interpretation of the EIO file?)
> If I fully autosize the system, E+ thinks that it should force:
> Calculated heating design air flow rate [m3/s], 4762.2.
>
> However, the actual flow rate is constrained by my input in the
> Direct Air objects to no greater than 0.2 m3/s. E+ seems to be
think
> the AHU needs to supply all the hot air in the zone. This forces
> mass oversizing of the flowrate in the boiler circuit.
>
> Therefore, I tried to force E+ strain of thought by using this?
>
> SYSTEM SIZING,
> A1:Loop, !- name of an AIR PRIMARY LOOP object
> sensible, !- type of load to size on
> 0.05144145, !- Design (minimum) outside air
> volumetric flow rate {m3/s}
> 1, !- minimum system air flow ratio
> 5, !- Preheat design set temperature {C}
> 12, !- Central cooling design supply air
> temperature {C}
> 20, !- Central heating design supply air
> temperature {C}
> noncoincident, !- Sizing Option
> Yes, !- Cooling 100% Outside Air
> Yes, !- Heating 100% Outside Air
> , !- Central cooling design supply air
> humidity ratio {kg-H2O/kg-air}
> , !- Central heating design supply air
> humidity ratio {kg-H2O/kg-air}
> Design day, !- cooling design air flow method
> , !- cooling design air flow rate {m3/s}
> flow/system, !- heating design air flow method
> 0.05144145; !- heating design air flow rate {m3/s}
>
> This corrects the boiler flowrates sizing problems however it
means
> that the convector units never turns on.
>
> Can anyone shed any light on how I might fix things? (or I do I
need
> to post some additional information)
>
> Kind regards
>
> -Elmer
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Everything you need is one click away. Make Yahoo! your home page now.
http://us.click.yahoo.com/AHchtC/4FxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/