Re: [EnergyPlus_Support] Zone heating loads and heating meter not equal
1. First, why is Heating:Electricity not equal to Boiler Electric Consumption?
Searching the .mtd output file for Heating:Electricity shows that Boiler
Parasitic Electric Consumption is also on that meter and reported by the boiler
as a separate value (not included in Boiler Electric Consumption).
2. Second, the boiler theoretical efficiency is 0.8. I presume you intended
something closer to 1.0. The BOILER:SIMPLE model does not explicitly compute
losses from the boiler to its surroundings, so this probably should be slightly
less than 1.0 for an electric boiler.
3. Third, the boiler "Minimum Part Load Ratio" (MinPLR) is set to 0.1.
3a. When the boiler has a load greater than zero, but less than 0.1, the
boiler will consume 0.1 of full-load power.
3b. The parasitic electric power is also adjusted by PLR (intended to model
load-dependent parasitics such as a draft inducer fan), but it appears there is
an error here. Even when the boiler load is zero, the MinPLR times the
parasitic load is being consumed. Only 7.5W in this case, but it shows up
every hour. A bug report will be posted for this.
3c. There are max iteration errors occuring, and there is an open CR related
to equipment MinPLRs and iteration problems. In this case (variableflow boiler
with varible speed pump and non-zero MinPLR) the problem is showing up.
Setting the MinPLR to zero eliminates the max iteration errors (reducing
execution time significantly).
4. There was a bug in version 1.2.3 (CR 6877) with variable flow plant loops
where temperatures did not always resolve completely. This is fixed in version
1.3.0. This has a minor impact, but can contribute to some differences.
So, with pump heat at zero, MinPLR at zero, and Efficiency at 1.0 (using
version 1.2.3), the coil load and boiler output agree within 0.1%, and the main
boiler electric consumption equals the boiler output.
Mike
On 26 May 2006 at 17:31, Sam Roose wrote:
> Setting the pump head to zero gives me 1.25 (instead of 1.06) and 0.52
> (instead of 0.47).
> I can see what you mean by the chiller COP varying now. The chiller output
> meets the chiller electricity * the chiller COP now.
> The boiler output is still some way form meeting the boiler electricity, and
> does not balance after a long time.
>
> So...
>
> Chiller Electric Power is virtually equal to cooling electricty
> Chiller electric power x COP is virtually equal to both (total zone cooling
> coil use + chilled water pump electricity) and chiller evap heat trans rate.
>
> However, Boiler electric power and Heating electricity are not quite equal
> and Boiler electric power is not close to equalling (total zone cooling +
> hot water pump electricity). Any ideas?
>
> Sam
>
> 5/26/06 5:10 AM, "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
>
> > Are you allowing for pump heat in the hot/chilled water loops? Try
> setting
> > the
> > pump head to zero to eliminate pump heat, then check again. Also, the
> chiller
> > efficiency is probably not constant (unless you are using the constant COP
> > chiller). First, check that the chiller evap heat transfer load matches
> the
> > coil loads (plus pump heat). Then look at the chiller COPs to see if the
> > electric consumption is reasonable. Also, if the chilled/hot water loop
> > temperatures are not maintaining setpoint at all times, there will be an
> > imbalance until the loop returns to setpoint, but the energy should
> balance
> > when summed over time.
> >
> > Mike
> >
> >
> > On 25 May 2006 at 18:05, Sam Roose wrote:
> >
> >> > I have just uploaded a file called "DESIGN_DAY_WEATHERFILE" that works
> >> fine,
> >> > except that the sum of the zone heating loads in the output file (total
> >> > water heating coil energy for 25 zones) does not equal the "Heating:
> >> > Electricity" meter, which is the same value as the boiler electricity
> once
> >> > converted to kWh. The same occurs with cooling (sum of total water
> cooling
> >> > coil rate vs cooling:electricity). With the file I have sent, the sum of
> >>
> the
> >> > heating coils is 1.06 of the heating meter (should be 1.00) and the sum
> of
> >> > the cooling coils is 0.47 (should be 0.33 due to a COP of 3 being
> used).
> >> >
> >> > I have noticed I can bring the zone heating load sum more into line with
> >>
> the
> >> > heating meter by changing the maximum and minimum supply temperatures in
> >>
> the
> >> > autosizing inputs, but the values diverge again if I make a major
> design
> >> > change.
> >> >
> >> > The file was set up in version 1.2.3
> >> >
> >> > Is the sum of the zone heating loads independent from the weather file?
> Is
> >> > there some other reason this occurs? Thanks in advance
> >> >
> >> > Sam Roose
> >> >
> >> >
> >> >
> >> >
> >> > The primary EnergyPlus web site is found at:
> >> > http://www.energyplus.gov
> >> >
> >> > The group web site is:
> >> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >> >
> >> > Attachments are not allowed -- please post any files to the appropriate
> >> folder
> >> > in the Files area of the Support Web Site.
> >> >
> >> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press
> >> the
> >> > "search" button.
> >> >
> >> > Yahoo! Groups Links
> >> >
> >> >
> >> >
> >> >
> >> >
> >> >
> >> >
> >> >
> >> >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate
> folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the
> > "search" button.
> >
> >
> >
> >
> > YAHOO! GROUPS LINKS
> >
> > * Visit your group "EnergyPlus_Support
> > <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
> > *
> > * To unsubscribe from this group, send an email to:
> > * EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
> > *
> > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
> > <http://docs.yahoo.com/info/terms/> .
> >
> >
> >
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
You can search right from your browser? It's easy and it's free. See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/