[EnergyPlus_Support] Re: humidity control
Mike,i report the system node temp and system node volflowrate,find
that system node temp is low enough(perhaps had achieved dew point)
but system node volflowrate remain max(sizing in eio).It seems that
the air loop capability is sized too small.Then i adjust the sizing
parameter to 2 and find it can control temp and hum well.I try
another model for a test,find it should set sizing parameter to 3 for
control aim.All is autosized in the model.Why is it sized so small?
Does it just sized the sensible load?But when i change the size type
in system sizing to total,the result did not change yet.
question 2 :I set 0.0094m3/s in the zone sizing for outside air and
oa method is flow/person.There is 20 people in the zone,min oa remain
1.So for all day,the outside air volflowrate should remain
0.188m3/s.But for simulation ,i find sometimes the outside air
volflowrate would increase.What caused this change?
question 3 :When i use vav:reheat,i set the vav outlet node temp in
winter to 16.I find in winter design day,the vav damper remain min
and the vav outlet node temp did not achieve setpoint temp.I checked
other simulation day,find that the vav outlet node temp did't not
achieved setpoint at all,sometimes are very small.Then it will be
reheated by reheat coil .How did the main heating coil and reheat
coil distribue the heating task?
Appreciated your kind help.
PCH
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "mjwitte" <mjwitte@...>
wrote:
>
> If you report the System Node Setpoint Temp at the air loop outlet
> node, you will see that the controller is trying to control to the
> specified RH setpoint, but the cooling coil is unable to supply air
> that is cold enough to meet this. I tried making some changes to
get
> this to autosize to a better result, but have not been successful
yet.
>
> Mike
>
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "hbn_pch" <hbn_pch@>
wrote:
> >
> > Dear,
> > I want to control humidity for a single zone.I create the
model like
> > the examplefile '5ZoneWaterCooled_HighRHControl.idf',but the Zone
Air
> > Relative Humidit was not controlled to setpoint in my model,while
the
> > examplefile can.
> > I really can't find the problems.appreciated your kind
help.I've
> > upload correlative file named 'RH CONTROL.zip'
> > Thanks very much
> > pch
> >
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
You can search right from your browser? It's easy and it's free. See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.