RE: [EnergyPlus_Support] Storey multiplier?



Hi, 

 

There are few ways you can deal with this.  

 

I use zone multipliers for buildings with four or more floors for faster
run times.  The simplest multiplier is in the Zone object, just multiply
each zone by a factor of 10.   In EnergyPlus, one can also group zones
into a list and multiply that list - usually used as a floor multiplier.
See the tips for multistory simulations in the Zone Group object
description in the I/O Ref. 

 

If you want to see an example input file of a model for 10 story
building, you can go to the new EnergyPlus Example File Generator and
request an input deck with 10 floors.   (These input files have three
floors with a single ground floor, a single top floor, and a middle
floor with multipliers.)   

 

If you really want your model to have all the surfaces for ten floors,
then it is easier if you use zone relative coordinates, you can copy and
paste the geometry without having to alter the geometry values in the
vertices-just shift the zone origins.  You still have to work out unique
names and the other side surfaces.   But be aware that you'll end up
with some pretty long simulation run times going this way.  

 

Brent

 

  

 

  _____  

From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Kevin Burke
Sent: Tuesday, June 27, 2006 11:07 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Storey multiplier?

 

Dear all,

I am a new user of EnergyPlus and I have defined a simply five zone
office building level with glazing on all sides and shading on all
sides. I want to make this one storey model a 10 storey model and I was
wondering if there is a way of copying this level and multiply the base
storey rather than having to copy and paste it ten times and replace the
Z geometry for all zones manually?

Regards,
Kevin


---------------------------------
Do you Yahoo!?
Next-gen email? Have it all with the all-new Yahoo! Mail Beta.

[Non-text portions of this message have been removed]

 



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/2pRQfA/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/