[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Cooling Room Temps in Zone without the help of an AHU
Hi Brent,
Sorry, that was a typo on my part, I meant to say load larger than -
13000 W (not KW). I get the following error...
** Severe ** Temperature out of bounds (-101.60) for
surface=WALL1
** ~~~ ** in Zone=TESTZONE
** ~~~ ** occuring in environment=LONDON - - - WMO#=- at
01/04 00:15
** ~~~ ** A temperature out of bounds problem can be caused
by several things. The user
** ~~~ ** should check the weather environment, the level of
internal gains with respect
** ~~~ ** to the zone, and the thermal properties of their
materials among other things.
** ~~~ ** A common cause is a building with no thermal mass --
all materials with
** ~~~ ** Regular-R definitions.
So this is why I'm abandoning that object and will look into radiant
cooling systems. What object would you suggest might give me a good
chance at getting decent control?
Kind regards
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent"
<brent_griffith@...> wrote:
>
> It could be expected with a huge number like -13 MW. Looking at
the
> code, I am not seeing any constraints on the value for power in
Electric
> Equipment. But the zone heat balance calculations do have some
limits,
> I would expect it to choke if the resulting zone air temps go
outside of
> a reasonable range (something like -20 to 50 C).
>
>
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Elmer
Morrissey
> Sent: Tuesday, August 29, 2006 10:33 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Cooling Room Temps in Zone
without the
> help of an AHU
>
>
>
> Hi Brent,
>
> I have tried using electrical equipment with negative numbers but
if
> I make the load larger than 13000 KW, then E+ throws up
unsuccessful
> errors. Is this to be expected?
>
> Kind regards
>
> -Elmer
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> , "Griffith, Brent"
> <brent_griffith@> wrote:
> >
> > That is a difficult one! Maybe a radiant cooling system could be
> made
> > to work along side the AHU.
> >
> >
> >
> > Another way would be to use Electric Equipment which works in
> reverse if
> > you put in negative values. But in order to meet a zone set
point
> you
> > would have to work out a pretty complicated and lengthy schedule
> for the
> > negative gains.
> >
> >
> >
> >
> >
> > ________________________________
> >
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of Elmer
> Morrissey
> > Sent: Tuesday, August 29, 2006 4:18 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > Subject: [EnergyPlus_Support] Cooling Room Temps in Zone without
> the
> > help of an AHU
> >
> >
> >
> > Hello all,
> >
> > Is there any way to maintain zone temps at 21C if I have an AHU
> that
> > MUST supply air at 26C into the zone at a certain rate?
> >
> > For instance, is there a 'chilled object' that would do what a
> > 'baseboard heater' would do but only in reverse.
> >
> > I would really appreciate any input.
> >
> > Kind regards
> >
> > -Elmer
> >
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.