Re: [EnergyPlus_Support] Should I model the plenum?



For calculating building energy consumption, modeling the plenums as 
separate zones is generally
not very important. There are cases where it will be important: 1 story 
building with a large roof area
and considerable outside air. For a multi-story office building it isn't 
important.

Fred Buhl

Michael J. Witte wrote:

>Should you model plenums?  It depends largely on the specific goals of the 
>analysis.  
>
>If you decide to ignore the plenums, you must make the conditioned zones tall 
>enough to include the plenum height so that the total area of exterior wall is 
>accounted for.  
>
>If you choose to model the plenums, then the plenum is modeled as a thermal 
>zone.  
>
>With EP-Quick it may be possible to create two buildings - one that is 7 
>stories with a floor-to-floor height of the conditioned space only, and then 
>another which is 7 stories with a floor-to-floor height of the plenum space 
>only, and then mix the two together.  All of the surface coordinates should be 
>OK except for the z values which could be easily modified to stack thing up 
>correctly.  Note that the plenum floors will come out of EP-Quick as multiple 
>zones, but these can be combined into a single zone simply be reassigning the 
>interior environment for the plenum surfaces and deleting the extra interior 
>surfaces that would be created in the plenum.  Well, it may not be a real 
>simple task, but it is doable.
>
>Mike
>
>
>On 1 Sep 2006 at 21:25, kir kumar wrote:
>
>  
>
>>Dear Mike,
>>    I have got a huge building with 7 floors, each floor is having a plenum.
>>All the return air from the zones enters the plenum before entering the air
>>handling unit in the mechanical room and this happens for every floor. One
>>side of the  air handling unit sucks the return air from the plenum and sends
>>fresh air from its other end into the supply duct as supply air to the
>>zones.
>>      My questions are 
>>  1. Should I model plenum as a separate zone?( I am actually using ep quick
>>to build my zones but unfortunately ep-quick does not have the capability of
>>building plenums)
>>  2. Should I just ignore the plenum and treat it as return air duct which
>>carries return air from zones to the air handler in mechanical room?
>> 
>>Can any one help me with those questions?
>>  thanks in advance,
>>kiran
>>
>> 				
>>---------------------------------
>> Here's a new way to find what you're looking for - Yahoo! Answers 
>> Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it
>>NOW
>>
>>[Non-text portions of this message have been removed]
>>
>>
>>
>>The primary EnergyPlus web site is found at:
>>http://www.energyplus.gov
>>
>>The group web site is:
>>http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>>Attachments are not allowed -- please post any files to the appropriate folder
>>in the Files area of the Support Web Site.
>>
>>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
>>"search" button.
>> 
>>Yahoo! Groups Links
>>
>>
>>
>> 
>>
>>
>>
>>
>>    
>>
>
>
>========================================================
>Michael J. Witte, GARD Analytics, Inc.
>EnergyPlus Testing and Support      
>EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>  
>


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/