Thanks, Mike. Creating a single branch worked.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> No, a bypass is not required. You say the "branches" (plural)
pass integrity
> testing. If you have the pump, the water heater and the pipe on
separate
> branches, do you have a splitter connecting the inlet branch to
the water
> heater branch? And a mixer connecting the water heater branch to
the exit pipe
> branch? If not, this is most likely the source of the errors.
>
> An alternative approach is to place the pump and the water heater
on a single
> branch (see example file TRHConstFlowChillerOneBranch.idf for a
similar case
> with a chiller and pump).
>
> Mike
>
>
> On 11 Sep 2006 at 19:05, chudson416 wrote:
>
> > Must the source side of a water heater:mixed necessarily have a
> > bypass? I am trying to model the supply side a heat recovery
loop
> > with a pump (as the supply inlet branch), a water heater (source
> > side), and an exit pipe. Although the branches pass integrity
> > testing, I receive a node connection error at the water heater
inlet
> > node with the statement that the inlet node did not find an
> > appropriate matching "outlet" node. Same is true for the supply
exit
> > pipe. In the supply side of the loop, I have 15 m/s flow in and
0 m/s
> > flow out. Any suggestions would be appreciated!
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/