[EnergyPlus_Support] No Design Heating Load



I am running a simulation where I have a compact vav system with hot 
water reheat.  I keep getting errors saying that I have no heating 
load for my interior zones, which makes me think that the outside air 
controls that I have on the system are not set up right.  I have set 
up outside air flow/person on the zone level for all zones in the 
building.  I was under the impression that the program uses these 
flows and max occupancy rates to determine the minimum outside 
airflow for each zone.  Is this true?

The exterior zones are not returing this error (Zone 1S is an example 
shown below), only the interior ones are (Zone 1SCore is an example 
shown below).  Anyone see a reason why I am getting zero heating load 
when I assume that the outside air flow/person is passed to the 
system level in the sizing routine?

Also, on the eio output, it says that the calc des air flow rate for 
these zones is zero, while the user des air flow rates are identical 
to the ones I entered.  

Thanks,

Andrew

   ** Warning ** Calculated design heating load for zone=1SCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=1NCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=2SCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=2NCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=3SCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=3NCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=4SCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=5NCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   ** Warning ** Calculated design heating load for zone=4NCORE is 
zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC 
inputs.
   
   
  
!-   ===========  ALL OBJECTS IN CLASS: COMPACT HVAC:ZONE:VAV 
===========   
   COMPACT HVAC:ZONE:VAV,
    1S,                      !- Zone Name
    VAV Sys Pat 1,           !- Air Handling System Name
    All Zones,               !- Thermostat Name
    autosize,                !- Zone Supply Air Max Flow Rate {m3/s}
    0.3,                     !- Zone Supply Air Min Flow Fraction
    flow/person,             !- Zone Outside Air Flow Type
    1.18000014980471E-02,    !- Zone Outside Air Flow Rate {m3/s}
    Hot Water,               !- Reheat Coil Type
    On,                      !- Reheat Coil Availability Schedule
    Reverse Action,          !- Zone Damper Heating Action
    ,                        !- Zone Supply Plenum Name
    ;                        !- Zone Return Plenum Name

COMPACT HVAC:ZONE:VAV,
    1SCore,                  !- Zone Name
    VAV Sys Office,          !- Air Handling System Name
    All Zones,               !- Thermostat Name
    autosize,                !- Zone Supply Air Max Flow Rate {m3/s}
    0.3,                     !- Zone Supply Air Min Flow Fraction
    flow/person,             !- Zone Outside Air Flow Type
    0.008024001018672,       !- Zone Outside Air Flow Rate {m3/s}
    Hot Water,               !- Reheat Coil Type
    On,                      !- Reheat Coil Availability Schedule
    Reverse Action,          !- Zone Damper Heating Action
    ,                        !- Zone Supply Plenum Name
    ;                        !- Zone Return Plenum Name
   
   
    
   
   
   
     ===========  ALL OBJECTS IN CLASS: COMPACT HVAC:SYSTEM:VAV 
===========

COMPACT HVAC:SYSTEM:VAV,
    VAV Sys Pat 1,           !- Air Handling System Name
    On,                      !- System Availability Schedule
    autosize,                !- Supply Fan Max Flow Rate {m3/s}
    autosize,                !- Supply Fan Min Flow Rate {m3/s}
    0.7,                     !- Supply Fan Total Efficiency
    600,                     !- Supply Fan Delta Pressure {Pa}
    0.9,                     !- Supply Fan Motor Efficiency
    1,                       !- Supply Fan Motor in Air Stream 
Fraction
    Chilled Water,           !- Cooling Coil Type
    ,                        !- Cooling Coil Availability Schedule
    ,                        !- Cooling Coil Setpoint Schedule
    13.1,                    !- Cooling Coil Design Setpoint {C}
    Hot Water,               !- Heating Coil Type
    ,                        !- Heating Coil Availability Schedule
    ,                        !- Heating Coil Setpoint Schedule
    13,                      !- Heating Coil Design Setpoint {C}
    0.8,                     !- Gas Heating Coil Efficiency
    ,                        !- Gas Heating Coil Parasitic Electric 
Load {W}
    None,                    !- Preheat Coil Type
    ,                        !- Preheat Coil Availability Schedule
    ,                        !- Preheat Coil Setpoint Schedule
    ,                        !- Preheat Coil Design Setpoint {C}
    0.8,                     !- Gas Preheat Coil Efficiency
    ,                        !- Gas Preheat Coil Parasitic Electric 
Load {W}
    autosize,                !- Maximum Outside Air Flow Rate {m3/s}
    autosize,                !- Minimum Outside Air Flow Rate {m3/s}
    FIXED MINIMUM,           !- Minimum Outside Air Control Type
    ,                        !- Minimum Outside Air Schedule Name
    Return air temperature,  !- Economizer Type
    NO LOCKOUT,              !- Economizer Lockout
    19,                      !- Economizer Upper Temperature Limit {C}
    4,                       !- Economizer Lower Temperature Limit {C}
    ,                        !- Economizer Upper Enthalpy Limit {J/kg}
    ,                        !- Supply Plenum Name
    ,                        !- Return Plenum Name
    Draw Through,            !- Supply Fan Placement
    ,                        !- Supply Fan Part-Load Power 
Coefficients
    Cycle On Any,            !- Night Cycle Control
    ,                        !- Night Cycle Control Zone Name
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness
    ,                        !- Latent Heat Recovery Effectiveness
    None,                    !- Cooling Coil Setpoint Reset Type
    None;                    !- Heating Coil Setpoint Reset Type
    
    
    
    
    
    
   
   
   






The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/