Re: [EnergyPlus_Support] Problem in Sensible Cooling Rate
Report variable "Zone/Sys Sensible Cooling Rate" (and similar variables)
reports the amount of cooling delivered to the zone by the HVAC system. I am
guessing that the HVAC system is not controlling the zone temperature in one of
both of these cases. Is the zone temperature the same in both runs?
Mike
On 27 Sep 2006 at 13:32, Apple Chan wrote:
> Dear all
>
> I had run EnergyPlus simulation for my simple model of an office building
> with window to wall ration of 0.5. When the glazing material is changed
> from clear glass to absorptive glass, the window transmitted solar (J) is
> reduced by about 30% which is very reasonable. However, there is almost no
> change in the sensible cooling rate. Could anyone please give me some
> advices on this problem?
>
> Many thanks!
>
> Apple Chan
> 27 Sep. 2006
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/