Re: [EnergyPlus_Support] A question on heat pump
It is controlled by the zone thermostat. The heat pump will try to provide
cooling when the thermostat calls for cooling, likewise for heating. One can
schedule individual coils, so it is possible to disable cooling or heating with
a schedule if desired.
Mike
On 28 Sep 2006 at 14:13, deserteagle_zhou wrote:
> Hi,all
>
> I was wondering which field controls the heatpump' cooling/heating operation
> mode. Or the
> modes are just shifted by the difference between the indoor air temperature
> and the setpoint?
> In my simulation module with a internal zone and four external ones, I put one
> heatpump per
> zone. I hope the heatpump in the internal zone can cool the space( wiht large
> heat gains) in
> the winter while others in outside zones are delivering heat.
>
> Thank you in advance.
>
> John
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/