>From the radiant slab expert . . . Mike
-----
Yes, the 2D calculation should be more accurate than the 1D simulation. The 1D
simulation spreads the calculated heat flux out over a plane which is probably
more appropriate for the resistance heating radiant systems. The 2D simulation
concentrates the heat source/sink on a line. This is more representative of
what is happening within an actual system. The 1D and 2D simulations will
yield the same surface temperature if the same flux is provided to both.
However, because generally the water temperature is similar between the two
models based on the plant controls. This will cause a difference in flux and
thus a different surface temperature. The 2D simulation is more accurate at
the cost of taking longer to calculate the conduction transfer function
coefficients that are needed to solve for heat transfer through the system.
-----
On 13 Oct 2006 at 1:46, Ian Doebber wrote:
> I compared the outputs between using the 1D and 2D for the radiant floor
> simulation. The 2D calculation determines a higher surface temperature and
> therefore lower cooling rate. Is the 2D calculation more
> conservative/accurate? What type of output differences should I expect
> between these calculations.
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup business
> systems are scanned for acceptability of content and viruses
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/