Re: [EnergyPlus_Support] Help! Can I use the Zone multiplier?
You can use the zone multiplier to expand the building; all it does is
multiply the load
sent to the HVAC system. If your original building had 1 air loop, the
new building will still have one
air loop. If everything is autosized the air loop flow rates, capacities
etc will increase to meet
the larger load.
Fred Buhl
well_kong wrote:
>I created a system include the Cooling water loop,condenser loop,
>Heating water loop and Air primary loop.I defined one floor as one Zone.
>Now One 3-floors building with HVAC is simulated sucessfully.
>But I want to expand it to 10 floors even 50 floors.Can I use the Zone
>multiplier? It also can multiply the HVAC devices automatically?
>
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
>Yahoo! Groups Links
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/