[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Zone Height
In EnergyPlus, surfaces have thickness for heat transfer, but they do not have
thickness for geometry. In most cases, the difference between inside and
outside dimensions is small, so use whatever dimension is most convenient from
the plans. The key is to end up with the correct amount of heat transfer area
from exterior to interior. For most medium to lightweight buildings, a good
rule of thumb is to use exterior coordinates for exterior walls and roofs,
interior coordinates for foundation floors, and centerline coordinates for
interior walls and ceilings. For a building with very thick massive walls,
then use centerline coordinates to achieve the correct amount of thermal mass.
Mike
On 15 Nov 2006 at 13:40, Thiago Karashima wrote:
> When inserting a roof over a zone, the height of this surface (z
> coordinate) which I must insert is the external height (including
> the thickness of the construction of the roof) or the internal
> height (from the floor to the internal surface of layer #4)?
>
> The roof construction is:
> Material 1, !-outside layer
> Material 2, !-layer #2
> Air space, !-layer #3
> Material 3; !-layer #4
>
> The same question I do for the corresponding walls. Which height do
> I have to use for the walls surrounding this zone?
>
> Thanks for your attention.
>
>
> Thiago Karashima
> Air-Conditioning and Refrigeration Laboratory - LaAR -
> www.laar.unb.br
> University of BrasÃlia - Brazil
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/