Pedro;

There is no separate object for the 2 pipe unit. Try using the 4 pipe 
unit and using the
hot and chilled water availability schedules to set the periods when the 
unit is using hot
or cold water.

Fred Buhl

Pedro Rodrigo wrote:
> Dear all,
> How can I model a two pipe fancoil system with constant volume of outside air in EnergyPlus?  The four pipe fancoil is available in the current version 1.4 but I didn´t find  the two pipe unit.
>  
> Pedro Manuel Rodrigo Cruz
> Universidad de Jaén
>
>
>
>
> 		
> ______________________________________________ 
> LLama Gratis a cualquier PC del Mundo. 
> Llamadas a fijos y móviles desde 1 céntimo por minuto. 
> http://es.voice.yahoo.com
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/