Chilled beams could be modeled as fan coils with zero fan power, since
their output is predominantly convective.
Phil
Michael J. Witte wrote:
> There are no chilled beam examples. It has been suggested that chilled
> beam
> systems can be modeled using the low temperature radiant
> system (with chilled water in the slabs) and then manually increase the
> convection coefficient on the ceiling surfaces (using the CONVECTION
> COEFFICIENTS object). For an example of radiant slab cooling systems, see
> ExampleFiles\RadLoHydrHeatCoolAuto.idf
>
> Mike
>
> On 1 Dec 2006 at 20:36, miaoworld wrote:
>
> > Currently I am trying to model the chilled beam system with
> > Energyplus. Did anyone has any examples or suggestions? Any
> > information would be appreciated.
> >
> > Thanks
> >
> > Miao.
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov <http://www.energyplus.gov>
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/>
> >
> > Attachments are not allowed -- please post any files to the
> appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com>
>
>
--
*****************************************
Philip Haves
Leader, Commercial Building Systems Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road Bldg 90R3111
Berkeley, CA 94720-8134
Tel: (510) 486 6512
Fax: (510) 486 4089
*****************************************
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/