[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Hotel: Unitary + PTAC Node Problem
You are getting confused with the node names for the PTHP inlet/outlet
and the air loop inlet/outlet node names. You have connected the PTHP
outlet node to the air loop and direct air unit through a node list.
Keep the node names for the PTHP inlet/outlet nodes separate from the
node names for the air loop. The direct air unit is the zone connection
for the air loop, not the PTHP. See the example file for
PackagedTerminalHeatPump for connection details. I suggest you write out
all example file node names for at least a single zone on a piece of
paper so you can see the connections more clearly.
Air Loop 1
|--------|
____|________|_____
| Zone1 Zone1 |
|Supply Return |
| Node1 Node |
| |
| Zone1 |_____
| Supply | |
| Node2 | |
| | PTHP1
| | |
| | |
| Zone1 |-----
| Exhaust |
| Node |
-------------------
PACKAGEDTERMINAL:HEATPUMP:AIRTOAIR,
Zone1EPTAC, !- Heat pump name
FanAndCoilAvailSched, !- Availability schedule name
Zone1E_PTACAirInletNode, !- Air inlet node name
>>>>Zone1E_PTACAirOutletNode,!- Air outlet node name
Zone1E_PTACOAInNode, !- Outside air node name
Zone1E_PTACExhNode, !- Relief air node name
Zone1E_PTACOAMixer, !- Outside air mixer name
autosize, !- Supply air volumetric flow rate during
cooling operation {m3/s}
autosize, !- Supply air volumetric flow rate during
heating operation {m3/s}
autosize, !- Supply air volumetric flow rate when no
cooling or heating is needed {m3/s}
autosize, !- Outside air volumetric flow rate during
cooling operation {m3/s}
autosize, !- Outside air volumetric flow rate during
heating operation {m3/s}
autosize, !- Outside air volumetric flow rate when no
cooling or heating is needed {m3/s}
FAN:SIMPLE:ONOFF, !- Supply air fan type
1E PTAC Supply Fan, !- Supply air fan name
COIL:DX:HeatingEmpirical,!- Heating coil type
1E PTAC DX Heating Coil, !- Heating coil name
0.001, !- Heating convergence tolerance
{dimensionless}
-8, !- Minimum outdoor dry-bulb temperature for
compressor operation {C}
COIL:DX:CoolingBypassFactorEmpirical, !- Cooling coil type
1E PTAC Cooling Coil, !- Cooling coil name
0.001, !- Cooling convergence tolerance
{dimensionless}
COIL:ELECTRIC:HEATING, !- Supplemental heating coil type
1E PTAC Heating Coil, !- Supplemental heating coil name
autosize, !- Maximum supply air temperature from
supplemental heater {C}
21, !- Maximum outdoor dry-bulb temperature for
supplemental heater operation {C}
blow through, !- Fan placement
ContFanCycComp; !- Heat pump operating mode
NODE LIST,
----1E Zone Equip Inlet, !- Node List Name
>>>>Zone1E_PTACAirOutletNode;!- Node_ID_1
DIRECT AIR,
1E Direct Air, !- Direct Air Name
COMPACT HVAC-ALWAYS 1, !- Schedule name for on/off schedule
----1E Zone Equip Inlet, !- Zone Supply Air Node Name
autosize; !- Maximum air flow rate {m3/s}
noelcrrl wrote:
> I am simulating a compact unitary system with PTAC units. The purpose
> of this is to model an HVAC system in a hotel. I have integrated both
> systems into the model, but I have encountered an error that I have
> not been able to resolve. It seems that I have improperly designated
> the zone air inlet nodes for each zone. I receive the following error
> for all zones with the compact unitary and PTAC combination:
>
> ** Severe ** Node Connection Error, Node="ZONE1E_PTACAIROUTLETNODE",
> The same node appears as a non-parent Outlet node more than once.
> ** ~~~ ** Reference Object=ZONE SPLITTER, Name=1E ZONE SPLITTER
> ** ~~~ ** Reference Object=COIL:ELECTRIC:HEATING,
> Name=1E PTAC HEATING COIL
>
> Any ideas on how to fix this? I have posted the file as a reference.
>
> File Description: Hotel: Unitary + PTAC Node Problem
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/