[EnergyPlus_Support] Re: Hotel: Unitary + PTAC Node Problem
Thanks Mike. Your advice did the trick.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> Just to further clarify, the CONTROLLED ZONE EQUIP
CONFIGURATION "Node List or
> Node Name: Zone Air Inlet Node(s)" field must be a NODE LIST name
which lists
> both the direct air and PTAC inlet nodes. So the quickest fix
lies in the
> CONTROLLED ZONE EQUIP CONFIGURATION and NODE LIST objects. For
example, for
> zone 1E
>
> ---- existing ------
>
> CONTROLLED ZONE EQUIP CONFIGURATION,
> 1E, !- Zone Name
> 1E Equipment, !- List Name: Zone Equipment
> 1E Zone Equip Inlet, !- Node List or Node Name: Zone Air
Inlet Node(s)
> . . .
>
>
> NODE LIST,
> 1E Zone Equip Inlet, !- Node List Name
> Zone1E_PTACAirOutletNode;!- Node_ID_1
>
> ---- Fixed ------
>
> CONTROLLED ZONE EQUIP CONFIGURATION,
> 1E, !- Zone Name
> 1E Equipment, !- List Name: Zone Equipment
> 1E Zone Equip Inlet Nodes, !- Node List or Node Name: Zone Air
Inlet
> Node(s)
> . . .
>
>
> NODE LIST,
> 1E Zone Equip Inlet Nodes, !- Node List Name
> 1E Zone Equip Inlet, !- Node_ID_1
> Zone1E_PTACAirOutletNode;!- Node_ID_2
>
>
> Mike
>
>
>
> On 5 Dec 2006 at 15:18, Richard Raustad wrote:
>
> > You are getting confused with the node names for the PTHP
inlet/outlet
> > and the air loop inlet/outlet node names. You have connected the
PTHP
> > outlet node to the air loop and direct air unit through a node
list.
> > Keep the node names for the PTHP inlet/outlet nodes separate
from the
> > node names for the air loop. The direct air unit is the zone
connection
> > for the air loop, not the PTHP. See the example file for
> > PackagedTerminalHeatPump for connection details. I suggest you
write out
> > all example file node names for at least a single zone on a
piece of
> > paper so you can see the connections more clearly.
> >
> > Air Loop 1
> > |--------|
> > ____|________|_____
> > | Zone1 Zone1 |
> > |Supply Return |
> > | Node1 Node |
> > | |
> > | Zone1 |_____
> > | Supply | |
> > | Node2 | |
> > | | PTHP1
> > | | |
> > | | |
> > | Zone1 |-----
> > | Exhaust |
> > | Node |
> > -------------------
> >
> > PACKAGEDTERMINAL:HEATPUMP:AIRTOAIR,
> > Zone1EPTAC, !- Heat pump name
> > FanAndCoilAvailSched, !- Availability schedule name
> > Zone1E_PTACAirInletNode, !- Air inlet node name
> > >>>>Zone1E_PTACAirOutletNode,!- Air outlet node name
> > Zone1E_PTACOAInNode, !- Outside air node name
> > Zone1E_PTACExhNode, !- Relief air node name
> > Zone1E_PTACOAMixer, !- Outside air mixer name
> > autosize, !- Supply air volumetric flow rate
during
> > cooling operation {m3/s}
> > autosize, !- Supply air volumetric flow rate
during
> > heating operation {m3/s}
> > autosize, !- Supply air volumetric flow rate
when no
> > cooling or heating is needed {m3/s}
> > autosize, !- Outside air volumetric flow rate
during
> > cooling operation {m3/s}
> > autosize, !- Outside air volumetric flow rate
during
> > heating operation {m3/s}
> > autosize, !- Outside air volumetric flow rate
when no
> > cooling or heating is needed {m3/s}
> > FAN:SIMPLE:ONOFF, !- Supply air fan type
> > 1E PTAC Supply Fan, !- Supply air fan name
> > COIL:DX:HeatingEmpirical,!- Heating coil type
> > 1E PTAC DX Heating Coil, !- Heating coil name
> > 0.001, !- Heating convergence tolerance
> > {dimensionless}
> > -8, !- Minimum outdoor dry-bulb
temperature for
> > compressor operation {C}
> > COIL:DX:CoolingBypassFactorEmpirical, !- Cooling coil type
> > 1E PTAC Cooling Coil, !- Cooling coil name
> > 0.001, !- Cooling convergence tolerance
> > {dimensionless}
> > COIL:ELECTRIC:HEATING, !- Supplemental heating coil type
> > 1E PTAC Heating Coil, !- Supplemental heating coil name
> > autosize, !- Maximum supply air temperature
from
> > supplemental heater {C}
> > 21, !- Maximum outdoor dry-bulb
temperature for
> > supplemental heater operation {C}
> > blow through, !- Fan placement
> > ContFanCycComp; !- Heat pump operating mode
> >
> > NODE LIST,
> > ----1E Zone Equip Inlet, !- Node List Name
> > >>>>Zone1E_PTACAirOutletNode;!- Node_ID_1
> >
> > DIRECT AIR,
> > 1E Direct Air, !- Direct Air Name
> > COMPACT HVAC-ALWAYS 1, !- Schedule name for on/off schedule
> > ----1E Zone Equip Inlet, !- Zone Supply Air Node Name
> > autosize; !- Maximum air flow rate {m3/s}
> >
> >
> > noelcrrl wrote:
> >
> > > I am simulating a compact unitary system with PTAC units. The
purpose
> > > of this is to model an HVAC system in a hotel. I have
integrated both
> > > systems into the model, but I have encountered an error that I
have
> > > not been able to resolve. It seems that I have improperly
designated
> > > the zone air inlet nodes for each zone. I receive the
following error
> > > for all zones with the compact unitary and PTAC combination:
> > >
> > > ** Severe ** Node Connection Error,
Node="ZONE1E_PTACAIROUTLETNODE",
> > > The same node appears as a non-parent Outlet node more than
once.
> > > ** ~~~ ** Reference Object=ZONE SPLITTER, Name=1E ZONE SPLITTER
> > > ** ~~~ ** Reference Object=COIL:ELECTRIC:HEATING,
> > > Name=1E PTAC HEATING COIL
> > >
> > > Any ideas on how to fix this? I have posted the file as a
reference.
> > >
> > > File Description: Hotel: Unitary + PTAC Node Problem
> > >
> > >
> >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/